    LP switch bypass timer



    Hey guys, i have just been challenged with the task of drawing a control diagram for an existing chiller, this unit has been modified so many times by so many people that I dont think the chiller knows what it is any more .

    My question is there have been 2 timers added to bypass the low pressure switch, is this normal and why would you need to?

    Also why does there never seem to be overload protection on compressors?

    Sorry for my ignorence but i am a Controls Engineer from Manchester, now living in Canada



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: LP switch bypass timer

    single phase hermetic compressors have a built in overload ;klixon;,as for the delay timer on the l/p can only guess its a preset l/p sealed switch so there to let it settle down?

  3. #3
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: LP switch bypass timer

    hi MF, in the old days ( before global warming) BGW, it was known for engineers to fit a cold winter pack ( CWP) this was a 2nd LP switch set 5 PSI higher than no,1 LP so on chilly mornings( which the UK + Canada ) do have. the new LP would trip and a timer would keep this ON for half an hour or so hope this helps =sedgy

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: LP switch bypass timer

    have contactors been replaced and some one omitted the overloads??
    as for the delay timers- they can be fitted to act as a delay on start up
    however- wouldnt it be better to fit an adjustable pressure switch without a delay
    whats the model of the chiller- check the original wiring diagram-see what should be in there, then maybe suggest additional safety devices.
    - surely a controls engineer should be able to answer a controls question?

    Quote Originally Posted by Mucking fuddle View Post
    Hey guys, i have just been challenged with the task of drawing a control diagram for an existing chiller, this unit has been modified so many times by so many people that I dont think the chiller knows what it is any more .

    My question is there have been 2 timers added to bypass the low pressure switch, is this normal and why would you need to?

    Also why does there never seem to be overload protection on compressors?

    Sorry for my ignorence but i am a Controls Engineer from Manchester, now living in Canada
    Last edited by Brian_UK; 13-08-2013 at 10:44 PM. Reason: square bracket

  5. #5
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: LP switch bypass timer

    LP switch with a bypass timer were normally fitted for low ambient conditions on older chillers

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: LP switch bypass timer

    As others has said above,
    The LP timer will prevent LP trips just after compressor starts, before the system reach a stable running condition. In my experience this would be set between 1/2 and 5 minutes.

    Either it is done to allow for starts at low ambient temperatures or sometimes it is to allow a higher than normal low pressure cut out. On some industrial chillers, the LP switch is also monitoring for a lack of flow or build up of ice in the evaporator, then the LP switch would be set just below the pressure at which the refrigerant's saturated pressure is at the freezing point of the cooled media. (0º C for water) but when the system first start to circulate the refrigerant it will take a minute or so before the pressure in the evaporator reach that cutout point, especially if it pumped down for shut off.


  7. #7
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: LP switch bypass timer

    Another thought, others has mention that this is old school, modern chillers often has the same function as the LP timer built in to their software. Sometimes it's an adjustable function in the menus of the controllers other times it is hidden in the background.
    About 2 years ago I even had the manufacturer's engineer out to look at brand new chiller that just been commissioned but kept dropping out on LP. He arrived late one Friday afternoon and stated on his report that "the chiller started an run OK". Looking at the key card log, he had spent less than 15 minutes on the roof. On his return visit (after repeated failures of the unit) he said that we must have a problem on the wet side as the chiller started up OK. Only after I cut the lead to the LP switch did he accept that there was a delay before the controls actually looked for LP faults. (On this particular chiller it was in the software to disregard the LP switch for 9 minutes after compressor start up)


  8. #8
    Join Date
    Aug 2013
    Location
    Canada
    Posts
    5
    Rep Power
    0

    Re: LP switch bypass timer

    Thanks for the help guys this is for a HVAC chiller on a telecoms room on a gas platform in the Atlantic, so cold mornings are a definate so much so we have had to heat trace the compressor . Compressors have built in thermal cut outs but it does not stop our client cooking them, the chiller was made by MARC controls in the USA and has never had overloads, as for controls engineer asking about controls i am used to process controls in the oil and gas industry, and also as previously said i am from manchester so i got my degree on the back of an embassy packet.LOL

  9. #9
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: LP switch bypass timer

    Embassy packet???

    In MANCHESTER???

    Must have been on the posh side!


  10. #10
    Join Date
    Aug 2013
    Location
    Canada
    Posts
    5
    Rep Power
    0

    Re: LP switch bypass timer

    Love it.

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: LP switch bypass timer

    lived here for 35yrs,dont know of any posh parts of manchester!!!- neither does google,bing !
    yahoo came up with this- i disagree with the answer as 1/2 the places are either on a sk postcode-cheshire or bl for bolton!!!
    http://uk.answers.yahoo.com/question...8180217AAcbPAz



    Quote Originally Posted by The Viking View Post
    Embassy packet???

    In MANCHESTER???

    Must have been on the posh side!


  12. #12
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: LP switch bypass timer

    So during those 35 years, how often have you seen a native smoking Embassy??


  13. #13
    Join Date
    Aug 2013
    Location
    Canada
    Posts
    5
    Rep Power
    0

    Re: LP switch bypass timer

    Sorry i am from Stalybridge, it used to be nice but then the bars took over, My lecturer smoked Embassy i could only ever afford Lambert and Butler

  14. #14
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: LP switch bypass timer

    staly vegas!!
    i remember a curry house opposite the bus station- threw up all over the place- was about 20yr ago!!
    im in audenshaw- bout 3 mile away!

  15. #15
    Join Date
    Aug 2013
    Location
    Canada
    Posts
    5
    Rep Power
    0

    Re: LP switch bypass timer