Thread: TXValve selection
-
13-08-2013, 09:39 AM #1
TXValve selection
001 (2).jpg
Hi Guys
I got this chart from work in a heap. looks an important piece of informaation but don't know how to interpret it or understand it. like how to make selection of orifaces and txvales for any system. what are the basic steps of selecting txvalves and orifaces for system by using catalog from suppliers etc.
Thanks
-
Re: TXValve selection
This should help. Pg 6
http://www.emersonclimate.com/Docume...C-141%20R7.pdf
-
13-08-2013, 02:01 PM #3
Re: TXValve selection
Before you choose the TXV, there is a lot of info you need to know:
Refrigerant in the system.
Evaporating temp.
Condensing temp.
Pressure drop on the TXV.
Flooded evaporator or not.
With MOP or without.
etc. etc.
Once you have gathered all the required info, it is time to mach the right TXV.
-
13-08-2013, 02:29 PM #4
Re: TXValve selection
ya it is a long process and no attention should be left unattended. correction factors and such but usualy if you follow the course they give on the catalog you will end up with a tolerable system that will opperate mostly as expected.
Now in Redvers Sask.
-
14-08-2013, 09:08 AM #5
Re: TXValve selection
Thanks guys for very useful knowledge . I have to read up on these things thoroughly now.
-
20-09-2013, 10:54 AM #6
Re: TXValve selection
Heat craft manual has a good info in valve & orifice selection .
Dd koranne