    Hi Guys
    I got this chart from work in a heap. looks an important piece of informaation but don't know how to interpret it or understand it. like how to make selection of orifaces and txvales for any system. what are the basic steps of selecting txvalves and orifaces for system by using catalog from suppliers etc.
    Thanks
  2. #2
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    232
    Blog Entries
    4
    Rep Power
    15
    Re: TXValve selection
  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    66
    Posts
    4,173
    Rep Power
    40
    Before you choose the TXV, there is a lot of info you need to know:
    Refrigerant in the system.
    Evaporating temp.
    Condensing temp.
    Pressure drop on the TXV.
    Flooded evaporator or not.
    With MOP or without.
    etc. etc.
    Once you have gathered all the required info, it is time to mach the right TXV.
  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    35
    Posts
    1,646
    Rep Power
    18
    ya it is a long process and no attention should be left unattended. correction factors and such but usualy if you follow the course they give on the catalog you will end up with a tolerable system that will opperate mostly as expected.
    Now in Redvers Sask.
  5. #5
    Join Date
    May 2012
    Location
    AUSTRALIA
    Age
    28
    Posts
    53
    Rep Power
    7
    Thanks guys for very useful knowledge . I have to read up on these things thoroughly now.
  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    68
    Posts
    400
    Rep Power
    13
    Heat craft manual has a good info in valve & orifice selection .