    I got a call from a customer about walk in cooler at one of her stores.
    We get to the site and its a Singer system from the late 70s but looks to be in good shape for 30+ years of use. The head master valve was wide open stacking refrigerant.
    Indoor coil info
    Make Singer
    MN: HDC150-1
    SN: 18-00916
    The TXV was stamped R500 with no other markings
    As per HeatCraft 15000 BTU 25*SST/10*TD "Evap is for cooler only as it has no heaters"
    Outdoor unit
    Make Singer
    MN/SN Tag missing
    Hand written tag on unit said R507
    Compressor Copeland EADB-0200-CAB
    Compressor is low temp R22/502 with 67000 BTU @ -25* evap / 105* cond
    Before starting work box temp was at 50*F
    Suction 60psi SH 70
    Liquid 345psi SC .78
    Shot off to supply house picked up a new
    1 - Sporlan Head Master OROA58058ODF
    1 - Emerson TXV HFE1RC 12000 BTU Med temp r404A
    2 - POE oil
    1 - Liquid Dryer
    1 - See All
    1 - Start cap
    1 - Run cap
    Back to customers store and do the good deeds. System started up and ran fine with below stats
    Indoor Unit
    28* Evap Air Discharge temp
    36.5* Evap Air Return temp
    19.8* TXV Dist tube 1
    13.2* TXV Dist tube 2
    21.8* TXV Dist tube 3
    19.5* TXV Dist tube 4
    26.8* Suction line temp
    108.4* Liquid line temp
    23* Evap surface at inlet
    26* Evap surface at outlet
    33* Box temp at stat
    71% RH
    Outdoor Unit
    85.2* Condenser Air inlet W/ 86% RH
    91.9* Condenser Air outlet
    48.7psi Suction
    26.4* Suction SH
    11.2* SC @ Receiver outlet
    7.6* SC @ Condenser outlet
    282.9psi Hot Gas
    23.5 Compressor SH
    128* Compressor Motor end temp
    102.5* Condenser face inlet temp
    93.5* Condenser face outlet temp
    At time of shut down
    30* Box temp
    10.6* SH @ Condenser
    47psi Suction
    281psi head
    Cycle time
    18min off
    24min on
    All was good until I put the cover back on the terminal box of the compressor, the next run cycle got about half way through and the thermal protector kicked out the compressor. I pulled a new one from the truck popped it in and the same thing 14min into the on cycle it kicked out on thermal. The compressor is pulling 7.84A and only shuts down with the cover installed...
    Thanks for any input given.
    SR
    Auckland
    74
    3,357
    38
    Re: Low Temp Skid on Med Temp Cooler,,, Mechanic going bald!!
    low temp system at medium temp application would be overloading compressor windings/current draw after extended run times. The klixon protector is being cooled by having terminal cover off . Fit a crankcase pressure regulator and limit actual compressor suction pressure. Better to replace compressor for a medium temp range.
    Aug 2013
    43
    4
    just to add
    104.2* LLT @ condenser outlet
    101.9* LLT @ receiver outlet
    40* RGT @ compressor
    Compressor listed for
    Evap/Cond -25/105
    RGT/LIQ 65 / 105
    I wonder if I up the SH so that it in the 20s when the unit hits the off cycle if the problem will subside, Is the motor passably getting over worked from the colder RGT. I did not record the SSH when the overload tripped but I will check this first thing in the morning.
    Aug 2013
    43
    4
    Missed your post when I put the last reply in, I was off in the data sheets and had the bing moment! but I think I was on the same track that you stated.
    I would love to replace the whole unit but customer does not want to spend the money.
    Aug 2013
    43
    4
    Fitted the unit with a CPR, Overload issue went away. Box pull down time is longer I just left the store and it was at 40* will check temp in the morning.