    Mycom screw no oil pump for 3 hours



    What do you think?

    A Mycom screw on NH3 -10sst +35 sct control system failure allowing it to run for 3 hrs with no oil pump.
    Safeties would not shut system down due to faulty control relay.
    Machine free to turn over & seems to run OK.



  2. #2
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: Mycom screw no oil pump for 3 hours

    How about this one.

    Guy on site wasn't wearing his glasses, pushed a bunch of buttons on the VSD to get the thing running, he succeeded - Manual ON but without condenser fans (thermosyphon oil cooling)...

    Ran all weekend, discharge temperature went off the dial at over +150°C & oil turned black.

    When the guys inspected the screw (Mycom 250) they needn't have bothered, it was fine inside.

    Forgot to say, no oil pump either..
    Last edited by HVACRsaurus; 11-08-2013 at 11:33 PM.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Mycom screw no oil pump for 3 hours

    Quote Originally Posted by HVACRsaurus View Post
    How about this one.

    Guy on site wasn't wearing his glasses, pushed a bunch of buttons on the VSD to get the thing running, he succeeded - Manual ON but without condenser fans (thermosyphon oil cooling)...

    Ran all weekend, discharge temperature went off the dial at over +150°C & oil turned black.

    When the guys inspected the screw (Mycom 250) they needn't have bothered, it was fine inside.

    Forgot to say, no oil pump either..
    Mycom's can be destroyed, but you really have to try, apparently!

  4. #4
    Join Date
    Jun 2009
    Location
    Canada
    Age
    55
    Posts
    82
    Rep Power
    15

    Re: Mycom screw no oil pump for 3 hours

    I spoke to Jerry at Mycom in Selma, Texas. He purposely tried to destroy one for R&D purposes. The machine finally packed it in at 7 psi oil pressure but what he found was, he had to throttle the oil valves to accomplish this. The differential pressure across the package provided enough oil pressure to keep the compressor running.

    This test was performed when they were designing the new screw packages with pre lube or no oil pump at all.

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Mycom screw no oil pump for 3 hours

    Hi, RANGER1

    Quote Originally Posted by RANGER1 View Post
    What do you think?

    A Mycom screw on NH3 -10sst +35 sct control system failure allowing it to run for 3 hrs with no oil pump.
    Safeties would not shut system down due to faulty control relay.
    Machine free to turn over & seems to run OK.
    It is possible ... in case of slide bearings there were some oil due to oil DP otherwise I doubt ... with roller bearings even with small oil wouldn't be a problem ...

    In the early days of STAL series 80 ... they run compressor for 1/2 hour without oil for test purpose and found out no problems ... info from the test person

    Industrial compressors are very rigid machines, but for sure they need lubrication ... and as always there are some extremes , but better to not investigate how far we can go ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Mycom screw no oil pump for 3 hours

    Thanks for replies, interesting to know what you can get away with to a certain degree.
    Discharge temp transmitter only goes to 100 C but went over that, to what temp do not know?
    Still running OK after fault rectified.