    HELP with: Evaporator and Condenser Surface Areas



    Hello,

    Domestic Refrigerators:
    Can someone please give me an evaporator and condenser surface area ratio please? Is the condenser usually larger in surface area than the evaporator?

    If you know the surface area for the evaporator and the condenser of any domestic sized refrigerator please can you pass on the information to me?

    A website link that showed all required dimensions to calculate surface area would also be great.

    Thank You



  2. #2
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    254
    Blog Entries
    4
    Rep Power
    20

    Re: HELP with: Evaporator and Condenser Surface Areas

    Surface area? Not sure what value that will be to you?

    Basic mathematics: http://www.basic-mathematics.com/sur...lar-prism.html

  3. #3
    Join Date
    Apr 2013
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: HELP with: Evaporator and Condenser Surface Areas

    Thanks passandscore for the joke, but I wanted a Value for the surface area of an 'Actual' Evaporator & Condenser, that someone on here would have worked with or studied. I am not having trouble with basic maths formulas (in this case).

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: HELP with: Evaporator and Condenser Surface Areas

    .

    Not set in stone but for a rough rule of thumb

    the evap is always 2/3 that of the cond.

    It's not surface area but it's a start point.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: HELP with: Evaporator and Condenser Surface Areas

    There are no rules for surface area, surface area has nothing to do with capacities. Volume should be a better value to compare but even then. What are your DT's, TE, TC, SH, SC...? All this will change the dimensions of your coil.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: HELP with: Evaporator and Condenser Surface Areas

    Surface areas are relevant to heat rejection/absorption in conjunction with temperature differences (dt) and duties.

    As with all calculations, you need to know 2 values to find the third. Just asking for a surface area ratio doesn't mean anything unless you know what the ratio is against.

  7. #7
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: HELP with: Evaporator and Condenser Surface Areas

    There is no surface ratio between condenser and evaporator. Condenser will be sized after sizing the evaporator and compressor. Capacity of air cooled condenser is based on total heat of rejection (THR).THR is equal to the evaporator capacity plus heat of compression.