    How do you guys calculate superheat?Heard a few different versions?
    Dec 2008
    Portugal
    48
    1,020
    Re: Superheat
    Read the saturation temperature, based on the pressure.
    Read the temperature on the thermometer
    Calculate the difference between temperature and the saturation temperature and you will get the superheat.
    The measure shall be on the same point.
    The pressure loss on the circuit decreases the pressure so also the saturated temperature which also contributes to the superheat increase.
    Feb 2007
    2,473
    45
    Re: Superheat
    As above, and if you take all your readings in degrees Celsius you will get your result in Kelvin (K) which is what normally is on the specifications from the manufacturers.