    Why the expansion valve is in the outdoor unit in split a/c?



    Im more curious about having the expansion valve in the outdoor unit in split a/c?
    It is more effiecient if it was on the indoor unit. (more subcooling and no vapourization of liquid in the luid line due to bad insulations)
    Can any one tell me the genuine reason?
    My opinion is that the static pressure drops in the vertical piping may result in flash gas and beacause of that they did this. Is it correct???



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    It is a capillary tube so all the pipes and inside unit are low pressure.

    Ac units, window and split were made at first to cool only and heating mode came much later so I guesss this is why.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    Also the balance of the liquid volume, in cooling mode all the liquid is contained in the outdoor unit so less is needed and in heating mode excess liquid is stored in the interconnecting pipe.

    And, if the EEVs were in the indoor unit you would still have the smaller interconnecting pipe after the EEV when the unit goes in to heating. Look at various makes of VRV/VRF, they got the EEVs in the indoor units or BS/BC boxes, then they need additional EEVs in the outdoor units and also expansion vessels.


  4. #4
    Join Date
    Apr 2013
    Location
    -
    Posts
    21
    Rep Power
    0

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    I was always told it was to reduce the noise made by the expansion device. If it was in the indoor unit it would be much louder!

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    .

    Two reasons in my opinion

    One is noise. Customers don't like the hissing sound
    some expansion devices can make.

    The other is ease of installation, who do you think
    installs the most AC units? People who are semi skilled
    or possess little or no skill. Imagine the Far East, Middle
    East, Asia and all the other warm places where the majority
    of AC units are sold and installed by people with little skill
    and no tools..

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    Chemi, it's at least 10 years now we could find unis with capillary tube. All have EEV's now.
    Noise was the main reason, then like The Viking said
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Jun 2013
    Location
    Sri Lanka
    Age
    31
    Posts
    2
    Rep Power
    0

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    Thank u guys & engineers...

  8. #8
    Join Date
    Jun 2009
    Location
    Scotland
    Age
    60
    Posts
    34
    Rep Power
    0

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    Fitting the expansion point on the outdoor unit enables the overall piping length to be increased from a system which contains the expansion point within the indoor unit. The use of capillary expansion enables the system to balance and thereby reduce the starting load on the compressor.

    tmm

  9. #9
    Join Date
    Jul 2013
    Location
    USA
    Posts
    58
    Rep Power
    11

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    Pretty much all the R22 and R410a units in the US have the TXV as part of the evaporator coil.

  10. #10
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    same here in Canada, or a piston orifice, never onces have I seen an EEV on a unit, and never the expansion device on the condenser side, mind you whole house splits are the most prevalent second only to window shakers
    Now in Redvers Sask.

  11. #11
    Join Date
    Jul 2013
    Location
    USA
    Posts
    58
    Rep Power
    11

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    Quote Originally Posted by The MG Pony View Post
    same here in Canada, or a piston orifice, never onces have I seen an EEV on a unit, and never the expansion device on the condenser side, mind you whole house splits are the most prevalent second only to window shakers
    Heat pumps do have a second TXV or capillary tube in the outdoor unit, but to be pedantic, when that is active, the outdoor coil is the evaporator.

  12. #12
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: Why the expansion valve is in the outdoor unit in split a/c?

    yup, built a few capilery heat pumps for fun, but notice I did say air cons thats about the only time we really see any thing in the out side unit!