    Perfection



    Gents & the Monkeys [Install & Spanner]

    question

    what would be the optimal pipe run ?

    Looking at installing Daikin RSX35J to FTXS35J


    Read through http://www.refrigeration-engineer.co...em-1-meter-run

    Chewed the fat with my split persona


    Dont like no reciever [over condensing [oops Mad Fridgie may shoot me for that term] or liquid slugging depending on conditions/mode]


    So am looking for the perfect pipe length for perfect running conditions with a 24*c - 32*c ambient

    ???

    R's xChillerman


    If the World did not Suck, We would all fall off !

  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Perfection

    all splits req a minimum 1-1.5mtr run- ive done units back to back and had to cut off the flare nuts on the indoor and braze 300mm of pipe to go straight on the condenser- any piperun over a few mtrs will affect performance, bends,restrictions, oil return- and knowing you if you flogged one of them fizzers and actually bought a 3.5 wall mount youd be ringing up daikin technical complaining about mass flow issues, heatloss thru lagging and inefficiency of an inverter compressor at low frequencies

    also dont remove any of the pre charged gas if u have a short piperun- it doesnt say it in the destructions !!!

    daikin suggest u sit in the lounge in the nack and sweat!
    Last edited by install monkey; 04-08-2013 at 05:06 PM.

  3. #3
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Perfection

    haha Thanx for the personal reference mate

    I'm just looking to get max life out of the pot

    If they say minimum pipe run of 3m & max 10m

    Then me thinking I best have nearer the 10m run than 3m

    As with no reciever to store the excess refrigerant

    Either subcooling needs to be high enough to allow the volume of the mass to be able to fit in the condenser/liquid line or excessive amount of refrigerant will be in the low side

    the second would surely cause however small over charge symptons

    its a bit hit n miss with this run length lark annit

    or is it just me

    R's xChillerman
    If the World did not Suck, We would all fall off !

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Perfection

    condenser acts as a reciever and lev is controlled to maintain ur 6 deg superheat. compressor frequency (loading - in a chillermans terminology) is regulated via discharge temp,compressor current and outdoor ambient,indoor freeze protection
    http://www.mediafire.com/download/dl.../ftyn35c_d.pdf
    have a flick thorugh
    cheaper option is feed ur cats to the dogs and sleep in the log cabin in ur garden!!!

  5. #5
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Perfection

    haha

    cheers thought there must be more to this than stoneage

    R's xChillerman
    If the World did not Suck, We would all fall off !

  6. #6
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Perfection

    Hey theres 246 pages !!!

    Will be back in quite a while

    R's xChillerman
    If the World did not Suck, We would all fall off !

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Perfection

    if you do part with money to purchase a unit, remember to a chiller dude- splits are work of the devil and black mans magic- so no sight glasses- i know you were tempted- no driers,isolation valves,oil traps,solonoids,and no widgets!

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Perfection

    http://www.daikin.co.uk/domestic/nee...tion/index.jsp
    before you comment on true air conditioning principals of heating/cooling and humidity control and air changes

  9. #9
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Perfection

    Quote Originally Posted by install monkey View Post
    if you do part with money to purchase a unit, remember to a chiller dude- splits are work of the devil and black mans magic- so no sight glasses- i know you were tempted- no driers,isolation valves,oil traps,solonoids,and no widgets!
    well you got my number with the drier , why cant I have one ?

    they certainly are work of the devil !

    frequency is varied only on load which is derived from room temp to set point

    it dont control subcooling and allow for the hit n miss scenario of pre charging for 3m-10m

    think I will be removing n adding charge once installed to find the perfect amount

    as a head start what is the amount you add for every metre over 10

    I can start by removing this for every metre under 10

    R's xChillerman
    If the World did not Suck, We would all fall off !

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Perfection

    4 meters is the optimal run.

  11. #11
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Perfection

    Quote Originally Posted by chemi-cool View Post
    4 meters is the optimal run.
    thanx Chemi

    saved me a lot of work there mate

    & it just so happens my run would have been between 3-3.5m so will just adjust the run to make it 4

    R's xChillerman
    If the World did not Suck, We would all fall off !

  12. #12
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Perfection

    In order to obtain the dependability of the compressor, the compressor must be stopped
    according to the conditions of the temperature of the outdoor air and outdoor heat exchanger.
    Detail 􀂊 Operation stop depending on the outdoor air temperature
    Compressor operation turns OFF under the conditions that the system is in cooling operation
    and outdoor air temperature is below –10°C (0°C for (A)RK(X)H, R(Y)N models).

    - hang on i'll stop here- better start checking of a 3.5kw chiller and a fan coil with 4 port actuator to control within .1deg

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Perfection

    Don't think you will have any problems with factory charge and 3-3.5m pipe run, accumulator will protect compressor from slugs imho.

    Got a panasonic inverter thats been ok for 8 years with 2m pipe run!
    Mostly found in Oxfordshire, UK :)

  14. #14
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Perfection

    he wouldnt have a problem if he mounted the condenser under the coffee table as the tight git wouldnt use it!

    Quote Originally Posted by monkey spanners View Post
    Don't think you will have any problems with factory charge and 3-3.5m pipe run, accumulator will protect compressor from slugs imho.

    Got a panasonic inverter thats been ok for 8 years with 2m pipe run!

  15. #15
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Perfection

    Quote Originally Posted by install monkey View Post
    In order to obtain the dependability of the compressor, the compressor must be stopped
    according to the conditions of the temperature of the outdoor air and outdoor heat exchanger.
    Detail Š Operation stop depending on the outdoor air temperature
    Compressor operation turns OFF under the conditions that the system is in cooling operation
    and outdoor air temperature is below –10°C (0°C for (A)RK(X)H, R(Y)N models).

    - hang on i'll stop here- better start checking of a 3.5kw chiller and a fan coil with 4 port actuator to control within .1deg
    Install you have totally lost me now wtf are you telling me ?

    Quote Originally Posted by monkey spanners View Post
    Don't think you will have any problems with factory charge and 3-3.5m pipe run, accumulator will protect compressor from slugs imho.

    Got a panasonic inverter thats been ok for 8 years with 2m pipe run!
    Thanx Jon

    you know me & the bond between me n a/c dont exist

    R's xChillerman
    If the World did not Suck, We would all fall off !

  16. #16
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Perfection

    floodback prevention during low ambient conditions

  17. #17
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Perfection

    oh I see cheers

    damn they made these things too compicated

    could run ok with relay, contactor n bulb thermostat with the correct charge

    huh can see this system being a experimental rig when that invertor board pops

    R's xChillerman