Results 1 to 11 of 11
  1. #1
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    high discharge temperature



    Hello
    Among some causes of too high discharge temperature in many articles there is mentioned low suction pressure. Among some causes of the LSP are named : low evaporator heat loads; frosted evaporator coils; evaporator fan out. How can the latter ones lead to increase of the discharge temperature ?



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: high discharge temperature

    Quote Originally Posted by Yuri B. View Post
    Hello
    Among some causes of too high discharge temperature in many articles there is mentioned low suction pressure. Among some causes of the LSP are named : low evaporator heat loads; frosted evaporator coils; evaporator fan out. How can the latter ones lead to increase of the discharge temperature ?

    Yuri,
    Possibly higher compression ratio as well as suction gas not cooling cylinders due to high superheat.
    The suction gas is also less dense.
    Mainly an issue with reciprocating compressors.

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: high discharge temperature

    Hi, Yuri B

    Quote Originally Posted by Yuri B. View Post
    Hello
    Among some causes of too high discharge temperature in many articles there is mentioned low suction pressure. Among some causes of the LSP are named : low evaporator heat loads; frosted evaporator coils; evaporator fan out. How can the latter ones lead to increase of the discharge temperature ?
    See this... link within passandscore answer .. a good article

    http://www.refrigeration-engineer.co...rge-temprature


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: high discharge temperature

    Thank you for your answers !
    But, the suction SH cannot be high, the returning gas is cool, with a capillary expansion device the gas is dense, the motor does less work and is less loaded, why the DT should increase ? The article does not explain this .

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: high discharge temperature

    Quote Originally Posted by Yuri B. View Post
    Thank you for your answers !
    But, the suction SH cannot be high, the returning gas is cool, with a capillary expansion device the gas is dense, the motor does less work and is less loaded, why the DT should increase ? The article does not explain this .
    I think it suggests compression ratio & volumetric efficiency. YOu say cool gas returning, but what is superheat & pressures at that time. Every situation is different so these are basic reasons. If you have a real life scenario we could be able to anylize things better. Leaking valves is another option.

  6. #6
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: high discharge temperature

    Quote Originally Posted by Yuri B. View Post
    Thank you for your answers !
    But, the suction SH cannot be high, the returning gas is cool, with a capillary expansion device the gas is dense, the motor does less work and is less loaded, why the DT should increase ? The article does not explain this .
    Have you check your system is perfect vacuum? Non condensable (air) will cause to increase the discharge temperature.

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: high discharge temperature

    Cpillar tube based systems shoud have the exact amount of refrigerant.

    Air in the system, partialy blocked drier, over charged system will raise the discharge pressure\temperature.

    you should recover the gas, replace drier, weigh the righe amount of refrigerant in.

  8. #8
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: high discharge temperature

    I should say I did not mean a particular case to resolve.
    Last edited by Yuri B.; 04-08-2013 at 06:19 PM.

  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: high discharge temperature

    Hi, Yuri B.

    Quote Originally Posted by Yuri B. View Post
    I should say I did not mean a particular case to resolve.
    In attached document, please, try to find your case ....


    Troubleshooting Mollier chart.pdf


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  10. #10
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: high discharge temperature

    If the discharge temperature elevates without rise the inlet superheat, this would indicate the problem of compressor mechanical trouble.

  11. #11
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: high discharge temperature

    Yes, and the efficiency - already mentioned here - drops in this case. However, worn out valves and what else is something different than "low load".
    Last edited by Yuri B.; 09-08-2013 at 07:00 PM.