Results 1 to 11 of 11
    Aug 2008
    Baltics
    56
    786
    10
    high discharge temperature
    Hello
    Among some causes of too high discharge temperature in many articles there is mentioned low suction pressure. Among some causes of the LSP are named : low evaporator heat loads; frosted evaporator coils; evaporator fan out. How can the latter ones lead to increase of the discharge temperature ?
    2,578
    29
    Re: high discharge temperature
    Quote Originally Posted by Yuri B. View Post
    Hello
    Yuri,
    Possibly higher compression ratio as well as suction gas not cooling cylinders due to high superheat.
    The suction gas is also less dense.
    Mainly an issue with reciprocating compressors.
    Jan 2006
    Croatia
    2,136
    Hi, Yuri B
    Hello
    See this... link within passandscore answer .. a good article
    http://www.refrigeration-engineer.co...rge-temprature
    Best regards, Josip
    Aug 2008
    Baltics
    56
    786
    10
    Thank you for your answers !
    But, the suction SH cannot be high, the returning gas is cool, with a capillary expansion device the gas is dense, the motor does less work and is less loaded, why the DT should increase ? The article does not explain this .
    2,578
    29
    I think it suggests compression ratio & volumetric efficiency. YOu say cool gas returning, but what is superheat & pressures at that time. Every situation is different so these are basic reasons. If you have a real life scenario we could be able to anylize things better. Leaking valves is another option.
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    43
    417
    Have you check your system is perfect vacuum? Non condensable (air) will cause to increase the discharge temperature.
    Sep 2003
    ISRAEL
    66
    4,152
    38
    Cpillar tube based systems shoud have the exact amount of refrigerant.
    Air in the system, partialy blocked drier, over charged system will raise the discharge pressure\temperature.
    you should recover the gas, replace drier, weigh the righe amount of refrigerant in.
    Aug 2008
    Baltics
    56
    786
    10
    I should say I did not mean a particular case to resolve.
    Jan 2006
    Croatia
    2,136
    Hi, Yuri B.
    In attached document, please, try to find your case ....
    Troubleshooting Mollier chart.pdf
    Best regards, Josip
    moideen's Avatar
    Apr 2008
    u.a.e
    43
    417
    If the discharge temperature elevates without rise the inlet superheat, this would indicate the problem of compressor mechanical trouble.
    Aug 2008
    Baltics
    56
    786
    10
    Yes, and the efficiency - already mentioned here - drops in this case. However, worn out valves and what else is something different than "low load".