    Hi everyone. This is my first post and new to this forum.
    I have a dry curing room I was servicing and the room won't come down to temperature.
    The room is 21 cubic meters and 3 - 5 deg. Set point
    The data on evap coil is 1.548 Frig/h 1,8 kw @ -12.5/+45 deg c (6139 Btu)
    2.236 Frig/h 2,6 kw @ -5/+40 deg c (8867 Btu)
    Suction pipe is 1/2" and liquid line is 3/8" and about 45' long going back to a rack system
    Tx valve - danfoss TES 5 with 0.5 orfice (I believe that is 3 ton) R404a
    The room can not hold temp and superheated is high with tx valve wide open. I believe suction line is undersized but will this cause this problem and what else can it be.
    Any help will be appreciated. Thank you



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Dry Rooms

    Problem with liquid feed, suction line seems OK.

  3. #3
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    254
    Blog Entries
    4
    Rep Power
    20

    Re: Dry Rooms

    What are your operating pressures? Superheat and subcooling temperatures?

  4. #4
    Join Date
    Sep 2010
    Location
    india
    Age
    43
    Posts
    6
    Rep Power
    0

    Re: Dry Rooms

    u r used wrong suction line size
    u can use 5/8 or 3/4 size suction line for that 45 feet length
    change it

  5. #5
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Dry Rooms

    hi I see ur expansion is not correct and u need a little more kw

  6. #6
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445