I have a dry curing room I was servicing and the room won't come down to temperature.
The room is 21 cubic meters and 3 - 5 deg. Set point
The data on evap coil is 1.548 Frig/h 1,8 kw @ -12.5/+45 deg c (6139 Btu)
2.236 Frig/h 2,6 kw @ -5/+40 deg c (8867 Btu)
Suction pipe is 1/2" and liquid line is 3/8" and about 45' long going back to a rack system
Tx valve - danfoss TES 5 with 0.5 orfice (I believe that is 3 ton) R404a
The room can not hold temp and superheated is high with tx valve wide open. I believe suction line is undersized but will this cause this problem and what else can it be.