Thread: Danfoss akc114
28-07-2013, 05:43 PM #1
Danfoss akc114
Hi all! I was hoping someone could tell me what to do! I have a danfoss akc114 but it is only putting out 10dvc at the akv valve. How can I get that raised to the 230dcv that the valve needs? All so the instructions are horrible. They dont tell you how to set the dip switches on or what the address codes are for. Can any one help me install this thing?
28-07-2013, 05:51 PM #2
28-07-2013, 09:34 PM #3
Re: Danfoss akc114
Going back a bit but that looks like the controllers Tescos used.
If so, need a handset to program them (unless there is an all singing front end fitted) and I think there was an option there for TEV or EEV in the menu.
Cheers,
29-07-2013, 12:54 PM #4
Re: Danfoss akc114
Hi JReefer,
You need a Danfoss AKA21 handset to set up this controller. I have attached a couple of docs to help!
AKC114B Quick Test Procedure.docMicrocool Controller Setup.docMICROCOOL SERVICE INFO.doc
The bit switches are for the controller address if it is on a network they are binary! switches 1-7 are for the address and 8 is for the internal clock and is set to on.
You cannot set anything without the handset!!
Regards,
Mel.Last edited by Silhouette; 29-07-2013 at 01:05 PM.
Mostly found nowadays at the sharp end of the stick!