    Copeland Scroll Compressor Problem



    Hi
    Dear friend we replace a 5 ton air conditioner compressor with copeland zr72 and after 24 hour the air conditioner showed error.
    compressor sounds was like sometimes that compressor has not any oil and after opening compressor we found that it has about 100 gram oil on it.
    after replace oil the compressor become very hot and use from 13 to 20 A and overload.
    we removed 4 way valve and it become full charged with R22 and use 11.4 amper but became very hot and has a bad noise.
    we check t air conditioner ohms and its normal (about 2.6).
    we think it has another restriction.
    what are you thinking about that?
    can this compressor work normal?
    How we can fix this problem?



  2. #2
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: Copeland Scroll Compressor Problem

    scroll compressor are known for their high working temperature
    then when u replaced oil
    u replaced it with same type oil or another
    with same quantity

  3. #3
    Join Date
    Apr 2008
    Location
    iran
    Posts
    9
    Rep Power
    0

    Re: Copeland Scroll Compressor Problem

    We replace it with 4GS oil.

  4. #4
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: Copeland Scroll Compressor Problem

    Quote Originally Posted by mehdi63 View Post
    We replace it with 4GS oil.
    what is the refrigerant type
    r22 r410a r407a
    then u put the same quantity

  5. #5
    Join Date
    Apr 2008
    Location
    iran
    Posts
    9
    Rep Power
    0

    Re: Copeland Scroll Compressor Problem

    Its R22
    Yes we put same quantity.

  6. #6
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: Copeland Scroll Compressor Problem

    what is the error code
    u checked the electric phase

  7. #7
    Join Date
    Apr 2008
    Location
    iran
    Posts
    9
    Rep Power
    0

    Re: Copeland Scroll Compressor Problem

    There is no error code.
    Only Compressor draw Amperage and overload and is noisy.
    Yes we chwcked electric phase.

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Copeland Scroll Compressor Problem

    4gs oil too thick, usually run copeland white oil or 3gs. It should say on the label the type and quantity of oil the compressor uses.
    Mostly found in Oxfordshire, UK :)

  9. #9
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Copeland Scroll Compressor Problem

    Quote Originally Posted by mehdi63 View Post
    Hi
    Dear friend we replace a 5 ton air conditioner compressor with copeland zr72 and after 24 hour the air conditioner showed error.
    compressor sounds was like sometimes that compressor has not any oil and after opening compressor we found that it has about 100 gram oil on it.
    after replace oil the compressor become very hot and use from 13 to 20 A and overload.
    we removed 4 way valve and it become full charged with R22 and use 11.4 amper but became very hot and has a bad noise.
    we check t air conditioner ohms and its normal (about 2.6).
    we think it has another restriction.
    what are you thinking about that?
    can this compressor work normal?
    How we can fix this problem?
    I think there is not proper oil return. Where the evaporator mounted is at higher position of compressor or below. If the evaporator lies above the compressor pump down cycle strongly recommended. If the evaporator were suited below the compressor, the suction must be trapped to ensure the oil return to the compressor.
    Whenever you replace any compressor, you had to study the cause of the compressor fail. when you replace the previous compressor, have you done any check?

  10. #10
    Join Date
    May 2012
    Location
    us
    Posts
    20
    Rep Power
    0

    Re: Copeland Scroll Compressor Problem

    Normal pressures coupled with high temp and over amperage sure points to high internal friction from failed bearings and trying to seize up. I am assuming pressures are normal? Obviously if you can reduce the charge to a minimum and still see an over current condition, it would be obvious the comp is toast but as Moideen said, you gotta learn why before replacement. Lack of oiling is a grenade with the pin pulled.

  11. #11
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: Copeland Scroll Compressor Problem

    What was the model # of the old compressor? Is it a proper replacement? Why did it fail?

    In R-22 applications “White Oil” is used. White Oil is compatible with Suniso 3GS, Texaco WF 32 and Fuchs KM.

    How often does the compressor cycle per hour? A high cycling rate will pump oil into the system and may lead to lubrication failure.

    Application Guidelines: http://www.heronhill.co.uk/pdf/industry4.pdf

    Replacement Guidelines: http://www.actrol.com.au//Global/Ass...ment-Guide.pdf

    Comparison between 3G & 4G Oil: http://www.sunoco.co.jp/english/product/gs/

  12. #12
    Join Date
    Apr 2010
    Location
    Qatar
    Age
    43
    Posts
    28
    Rep Power
    0

    Re: Copeland Scroll Compressor Problem

    Replaced Another Compressor & give a Correct phase Sequence ..... This Compressor Is Gone Now. Try to find out the reason Why Comp Oil Flushing out from Compressor ...... The Last Compressor Original one how many moths was run?