Thread: Fan flow
    Jan 2006
    Port Adelaide
    52
    Fan flow
    Hi guys.
    I was running a few tests today and was just wondering what your speculations would be
    Constants. Fan motor, pwr supply, air baffle, refrigerated space, ambient, test equiptment.
    I start with a 20inch fan and matching cowl and measure Watts, Amps, M3/Hr and Rpm.
    What will happen to these values if I increse firstly the blade and cowl diameter by 1 inch?
    Then increase the pitch.
    And decrease the pitch.
    I have results but would like your speculation.
    Feb 2006
    Estonia
    10
    Re: Fan flow
    If you increase the diameter of the fan, the result depends on fan motor characteristics. If the motor didn't work on its limits, the m3/h, watts and amps will increase. If the motor had optimal load before increasing the fan diameter, the m3/h stay constant or decrease, the Watts and Amps stay constant or increase.
    Sep 2005
    uk
    499
    21
    Re: Fan flow
    Quote Originally Posted by hybridjunction
    Hi guys.
    speaking from a speculative point of view, i think your fan may speed up or slow down. there is also the possibility that the volume of air moved by the fan may increase or decrease. further speculation leads me to believe that if you reverse the direction of the motor it may blow air in the other direction to the first direction in which it was directed.
    Takes a licking, keeps on ticking.
    Dec 2004
    LEBANON
    44
    854
    21
    Re: Fan flow
    It's simple , using the same fan but changing a parameter and see how this affects the other parameters, can be done by using the "Rateau" simulation (similitude) formulas (if you consider that the air density is unchangable between the inlet and the outlet of the fan).
    If you need more information please let me know
    Jan 2006
    Port Adelaide
    52
    Re: Fan flow
    Quote Originally Posted by slingblade
    That is very speculative slingbade thanks.
    Jan 2006
    Port Adelaide
    52
    Re: Fan flow
    Quote Originally Posted by botrous
    Hi botrous, my tests were based working with the fan itself. I've not heard of the "Rateau" simulation formulas.
    If you could elaborate, it would be appreciated.
    I'm new to Refrigeration, yet to do second block of training. So These formulas would give great insight.
    Hybridjunction
    Jan 2006
    Port Adelaide
    52
    Re: Fan flow
    Anyway, It was found that increasing dia by 1 inch gave less air flow, slower revs, same amps and higher wattage; but when the pitch was increased 8 deg, wattage acually was lower than the former and air flow was greater.
    When it came to a load test though, the larger fan with greater pitch failed.
    It was put down to the air distribution characteristics.
  1. flow switch connection
    By afeef in forum The Trail of Tears
    Last Post: 23-12-2009, 06:55 PM
  2. Replies: 15
    Last Post: 24-10-2002, 06:52 PM
  3. Not enough air flow
    By coolsights2000 in forum Technical Discussions
    Last Post: 22-07-2002, 06:35 PM
  4. Accidental Release Flow Rates
    By mbeychok in forum Industrial
    Last Post: 20-11-2001, 12:53 AM
  5. Accidental Release Flow Rates
    By mbeychok in forum Tools and Calculators
    Last Post: 20-11-2001, 12:45 AM