    Talking Apac s14 hp/chb-02 drc



    Hey Felas

    Ive got heating problem on this apac drc unit. seems to blow cold air on startup after off cycle or defrost. Any ideas? Yes the fan is set to cycle off at setpoint to.

    Cheers!



  2. #2
    Join Date
    Oct 2009
    Location
    Sydney
    Age
    38
    Posts
    69
    Rep Power
    15

    Re: Apac s14 hp/chb-02 drc

    for how long? it takes a while for the coil to heat up....

    the w
    ay apacs are set up, it will cycle the indoor fan with the compressor on heating mode, so when the compressor starts, the fan will start, and the indoor coil doesnt heat up instantly....

    some br
    ands will have a pcb in the indoor unit that will have a sensor on the indoor coil, so it wont run the indoor fan until the coil gets warm. what sort of controller have you got?

    u could
    always get something retrofitted onto it that will do the job, like a hanwest controller, but it depends how much it is worth to you....