    Thumbs up An important issue of "Refrigeration Discharge Pressure"



    Hi Fellows

    Refrigeration discharge temperature is determined by the condenser's capacity to reject heat. When the condensing pressure goes below a minimum pressure setting, selected by operators, condenser fans turn off. This reduces condenser capacity and prevents the temperature and associated pressure from going below the set point. Compressors require less energy to operate against low discharge pressures, but to reduce this discharge pressure, the condenser fans must operate more frequently. As condenser fans typically use significantly less energy than the compressor, reducing compressor use can lead to significant energy savings. Reducing compressor discharge pressure saves approximately 1% of compressor energy consumption for each degree Fahrenheit reduction of condensing temperature. ButOften there are specific applications that drive the need for high pressure set points. Below is a list of four common reasons for having such set points and how they can be fixed.

    1. Liquid Injection Cooling typically consumes 5-15% of the compressor power to recompress injected refrigerant and is used to cool the compressor. Install thermosyphon oil cooling to avoid power and energy costs associated with liquid injection oil cooling. Thermosyphon cooling does not consume compressor power.

    2. Expansion Device Design can lead to higher required discharge pressures. By looking into different designs, having your system evaluated and selecting components that operate well with lower discharge pressure, the efficiency of your refrigeration system can be improved.

    3. Moving Refrigerant to Distant Endpoints can lead to a need for higher discharge pressures to ensure refrigerant can reach its destination. By installing liquid pumps in the system, discharge pressure can be reduced while still serving the entire refrigeration system.

    4. Hot Gas Defrost is sometimes used to defrost evaporators as needed and requires a high discharge pressure. We suggest only raising the discharge pressure when needed for hot gas defrost and letting the discharge pressure drop lower otherwise, or using another defrost strategy such as applying warm process water. Check to make sure your facility does not require high pressure set points for special applications before making alterations to your process or equipment.

    Good Luck.
    Last edited by Josip; 08-08-2013 at 06:06 PM. Reason: sorting



  2. #2
    Join Date
    Aug 2009
    Location
    Iran
    Age
    33
    Posts
    12
    Rep Power
    0

    Re: An important issue of "Refrigeration Discharge Pressure"

    I wrote pretty regularly, but unfortunately this was the case.

    This may be due to being a novice.

    Excuse...

  3. #3
    Join Date
    Sep 2011
    Location
    USA
    Age
    45
    Posts
    84
    Rep Power
    14

    Re: An important issue of "Refrigeration Discharge Pressure"

    Lot's of good points in this. There is always a lot of misconceptions
    around low condensing temp.

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: An important issue of "Refrigeration Discharge Pressure"

    yup and the head aches of keeping a well tuned system, I use balanced port txv's which allow for lower head pressure while maintaining good function, and then use the VG47-AA head modulating valves to fix the head pressure to the ideal level, or a transducer driven vfd to drive the condensing fan at optimum.

    higher initial cost but superior year round unit efficiency, but most penny wise pound foolish, they just want the cheapest plant now and running cost is ignored totally!

    That is the hardest part of our jobs, to explain why the initial cost all be it high will save them the most money in the long run by being much more efficient energy wise, and due to lower pressures easier on the mechanical systems resulting in a higher mean time between failure rating!
    Now in Redvers Sask.

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: An important issue of "Refrigeration Discharge Pressure"

    Quote Originally Posted by Rahju View Post
    I wrote pretty regularly, but unfortunately this was the case.

    This may be due to being a novice.

    Excuse...
    Sorted ... I do believe ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  6. #6
    Join Date
    Aug 2009
    Location
    Iran
    Age
    33
    Posts
    12
    Rep Power
    0

    Re: An important issue of "Refrigeration Discharge Pressure"

    Sorted ... I do believe ...