Results 1 to 6 of 6
Thread: Daikin Error JH
-
20-07-2013, 11:25 PM #1
Daikin Error JH
New to Daikin. Searched the forums, found the code, but no experience of what needs to be done.
Code JH, Oil thermistor. Its an old VRV system, but working fine last year. Cant find a specific manual. And experience or thoughts?
-
21-07-2013, 12:05 AM #2
Re: Daikin Error JH
whats the model number?
-
21-07-2013, 12:52 AM #3
Re: Daikin Error JH
Paul
It's the sensor or possibly the PCB needs replacing. Contact your air conditioning contractor who can confirm and order as necessary. If you don't have anyone then I can do it as Northampton isn't too far and I'm often in Silverstone...
-
21-07-2013, 09:03 PM #4
Re: Daikin Error JH
This is a faulty Oil Temperature Thermistor usually R5T.
This fault is produced if the PCB cannot read any information from the thermistor suggesting that it is either fully open or closed circuit. This thermistor can be checked with a multi meter for a resistance value
-
22-07-2013, 04:17 PM #5
Re: Daikin Error JH
Its a RSXY8.
Thanks I'll check the resistance.
-
05-08-2013, 10:21 AM #6
Re: Daikin Error JH
Yep , it was the Thermsiter. Thanks