Thread: TAE EVO 015 chiller manual
20-07-2013, 11:03 AM #1
Chaps I have mislaid the manual for this old 98 chiller. It's shows the tap with a cross led error and AAAi on the displayDSC06252.jpgDSC06251.jpg anyone has this it would really help
20-07-2013, 01:01 PM #2
Re: TAE EVO 015 chiller manual
Hi richard
I will email the complete manual, which is not the same exact model.
But would appear close enough.
Basically
The tap indicates low water level in the tank!
AAA1 is with led L4 & L8 = LP sys1
L4 & L9 = LP sys2
Quite logical if the water level is low.
Good luck Grizzly
20-07-2013, 02:32 PM #3
I guessed it may be something like tht but the tank is full to the brim which confuzzed me
20-07-2013, 03:01 PM #4
We all get confuzzed, especially in this heat.
I would be looking for poor heat load or faulty readings /transducer etc.
Basically relavent to what would normally indicate low level?
good luck.
20-07-2013, 03:31 PM #5
It was late Friday and I had an appointment to go to so we'll be back Monday with this information Thanks as ever
20-07-2013, 06:58 PM #6
got one of them jobbies in widnes- they have a header tank on the back with isolation valve underneath- on ours the pipework goes above the tank so its pointless- anyway,theres a manual air vent on the back of the evap shell
30-07-2013, 03:45 PM #7
blockage in the fill hose. played about and job's a good'en
