Results 1 to 7 of 7
  1. #1
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    TAE EVO 015 chiller manual



    Chaps I have mislaid the manual for this old 98 chiller. It's shows the tap with a cross led error and AAAi on the displayDSC06252.jpgDSC06251.jpg anyone has this it would really help



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: TAE EVO 015 chiller manual

    Hi richard
    I will email the complete manual, which is not the same exact model.
    But would appear close enough.
    Basically
    The tap indicates low water level in the tank!
    AAA1 is with led L4 & L8 = LP sys1
    L4 & L9 = LP sys2
    Quite logical if the water level is low.

    Good luck Grizzly

  3. #3
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: TAE EVO 015 chiller manual

    I guessed it may be something like tht but the tank is full to the brim which confuzzed me

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: TAE EVO 015 chiller manual

    We all get confuzzed, especially in this heat.
    I would be looking for poor heat load or faulty readings /transducer etc.
    Basically relavent to what would normally indicate low level?
    good luck.
    Grizzly

  5. #5
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: TAE EVO 015 chiller manual

    It was late Friday and I had an appointment to go to so we'll be back Monday with this information Thanks as ever

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: TAE EVO 015 chiller manual

    got one of them jobbies in widnes- they have a header tank on the back with isolation valve underneath- on ours the pipework goes above the tank so its pointless- anyway,theres a manual air vent on the back of the evap shell

  7. #7
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: TAE EVO 015 chiller manual

    blockage in the fill hose. played about and job's a good'en

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •