    superheat



    so to avoid confusion i thought i would explain on here and see if you guys agree ,when you take a super heat reading what you are essentially measuring is how much heat the refrigerant is picking up from the outlet of the evaporator to the inlet of the compressor ( the amount of heat added after the refrigerant has boiled off) but i see technicians taking the suction pressure and converting it to temperature and then i see them take a reading of the suction line in near enough the same place as the service port ! this to me is wrong your not measuring the amount of heat picked from outlet of evap to inlet of compressor. Now say for example i take my suction pressure near the inlet of the compressor and convert it to temperature which is r410a -121 psi corresponding to 35 f (meaning that at that point in the suction line my refrigerant at that pressure is 35 f). Now lets say you dont have a service port at the immediate outlet of the evaporator you measure the suction line temp with thermocouple as close to txv bulb as possible making sure its insulated now lets say thats the temperature reading you get is 20f the difference between both temps is 15 f which is your superheat ( the amount of heat picked up after the refrigerant has boiled off between the outlet of the evaporator and the inlet of the compressor. Any comments welcome thankyou



  2. #2
    Join Date
    Sep 2011
    Location
    USA
    Age
    45
    Posts
    85
    Rep Power
    14

    Re: superheat

    Superheat is measurment between the refrigerant boiling point(Saturated Suction Temp) and the temperature of the refrigerant vapor. Both at the outlet of the evap and the inlet of the compressor you are still taking a superheat reading, just at different points. If you are just taking it at the compressor it may not give you an accurate idea of how your evap is working depending on length of suction line, ambient condition suction line is running through, insulation condition ect...

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: superheat

    You new guys enjoy your post!

    If you bothered to search the topic, you will find numerous previous answers and debaits!

    Grizzly

  4. #4
    Join Date
    Jul 2013
    Location
    Wales
    Age
    37
    Posts
    2
    Rep Power
    0

    Re: superheat

    so my suction pressure corresponding to 35f is the temperature at which it will boil at that given pressure and not the actual temperature of the refrigerant so thats why u take a suction pipe reading? is that what your saying?

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: superheat

    Also please try and use the SI system it makes life so much easier for us old folks.

    However, having said that, this link being an American product is still in °F.

    Have a look at the diagram on page 4 and it should explain things for you.

    Download the first document ref no. 10-135

    http://sporlanonline.com/literature-...nal-materials/
    Last edited by Brian_UK; 15-07-2013 at 11:15 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015