    lennox r410a heat pump



    hi friends i have a problem with this chiller. This week its been very hot about 30c ambient temperature.got a call out to see why wasnt working.got site and found c1 fans not comming on and c2 empty of gas.the fan inverter wasnt sending any power to fans its a altiver 21.so by pass it and ran fans direct and it ran for 2.5 hours good. Brought temp from 36c to 14.8c and then the pressure unit its armstrong went out on fault and shut the chiller down on bms.refilled the pressure unit got pressure upto.0.9b and restart the chiller. It ran for 20 minutes and it went off again on pressure unit.found the bladder empty of pressure so pumped air into the bladder and fill it up with water again. But still shows fault on bms and chiller wont run. The chiller has it own electronic flow switch and customer has sontay pressure switches. The water flow is 2bar in and 1.5 bar out of evaporater.the chiller shows on service display is unit on. Enabled c1. Comps waiting flo. Switch on. Hp off lp on. Im stuck on what to do next.how to get it going or how to by pass bms. any help will be great ful



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: lennox r410a heat pump

    http://www.mediafire.com/download/hi..._14_LENNOX.pdf
    has the expansion vessel bellows held at 1 bar or has it leaked back into system?

  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: lennox r410a heat pump

    Hi the xpansion vessels bellows pump upto 8 psi and unit water pressure upto 1.2 bar. But im going back tomorrow and try again. Is there any way to by pass these things to run the chiller for few seconds just to prove the chiller is ok

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: lennox r410a heat pump

    bms can be bypassed - usually its just a remote on/off signal and a common fault signal. check external wiring going into the chiller.
    check control panel for bms for chiller relay- maybe manually latch it to enable output

    pressurisation unit will only alarm on hi/low pressure and constant fill-leak prevention- as long as ur system is between 1-3 bar shouldnt be an issue

  5. #5
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: lennox r410a heat pump

    Thankyou friend

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: lennox r410a heat pump

    does the chiller have a dc50 controller- because you would need a ds50 service tool to reset a major alarm- and also easier for reading alarm history and thermister values

  7. #7
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: lennox r410a heat pump

    Yes it does have a ds 50 service controller and ive reset all alarms on it and when you check rhe comps it say comps wait.flow,state on

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: lennox r410a heat pump

    state on - signal for comp run- unless external safety devices holding it off- pressure switch/flow switch

  9. #9
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: lennox r410a heat pump

    Im there tomorrow morning again and ill give an update to what has happen

  10. #10
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: lennox r410a heat pump

    Hi install its the carel pco board that isnt sending signal. Got lennox comming out to replace soon.thankyou for your help friend

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: lennox r410a heat pump

    Ghaz, your avatar is an opened Bitzer. Why you opened it? We have a similar machine with exploded oil filters in the compact screw.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: lennox r410a heat pump

    An it's also in a Lennox but on R407c
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: lennox r410a heat pump

    Hi peter my picture is of an csh 85 bitzer i open it to change the oil seperater o ring and internal oil filter because the previously motor burnt on it

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: lennox r410a heat pump

    Was the machine old and ran it a lot of hours? Did your rewind the motor?
    We have on a Lennox now in 4 years 5 burnt compressors
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: lennox r410a heat pump

    Yes machine wasnt that old it was on r407c gas wirh water pumps built on chiller and 2 times pump fail and then on circuit 2 two compressors burn out and finaly the evaporater had burst it copper tubes and the chiller got scrapped