    Never to old to learn!



    Hi Guys!
    Working on an Ice plant today that had more than a few issues, including several Small wispy leaks.
    Having repaired the leaks.
    One of the hot gas lines had a Danfoss solenoid coil (EVRA 20) which had burned out.

    Having replaced the coil for a new one and discovered a loose neutral, there were still issues?

    Which was found by my esteemed colleague.

    The brass terminals (which clamp the supply cable) had turned blue/green
    Causing a high resistance within the connections, which cause the coil to malfunction.


    Ain't seen that one before!
    The combination of moist damp air and ammonia (albeit a small amount) within the area.
    Was the perfect breeding ground for copper oxide (or a blue green scale?)

    Changed the Terminal box and all was good!