    Re: Transmission wiring on Daikin VRV2

    Quote Originally Posted by frank

    This won't work. If you add additional indoor units or change a PCB you must reset the system to redefine the communication loop.
    We have found this out the hard way

    you can initially set the system up by switching on in a sequence that you require. But as frank states the problem arises if you need to modify later.

    Supermarket networks are the same, although some controller manufacturers allow radials on the network, I advise our guys to daisy chain, it's just easier in the long run

    Kind Regards. Andy
    Last edited by frank; 28-02-2008 at 08:34 PM.

  2. #2
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Transmission wiring on Daikin VRV2

    Can only say that i have seen systems that have been wired with star points all over the place, some times the system works other times it dont. So the lesson is dont star point. Oh and dont use screened cable its just going to lead to problems!

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Daikin vrv control wiring
    By Jase in forum Air Conditioning
    Replies: 4
    Last Post: 23-03-2011, 04:01 AM
  3. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM
  4. Daikin problem
    By Jambo in forum Trouble Shooting
    Replies: 4
    Last Post: 28-07-2006, 07:42 PM
  5. Daikin VRV2 Recharging
    By Birds in forum Air Conditioning
    Replies: 5
    Last Post: 25-06-2006, 12:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •