parallel TXV
Would it work to connect two TXVs in parallel and use them as one big TXV?
09-07-2013, 08:48 AM #2
Re: parallel TXV
Yes it will work. By the way what is the application you are asking for ?
Sendhil
09-07-2013, 08:57 AM #3
09-07-2013, 11:12 AM #4
Re: parallel TXV
It would work if you fed them into a distributor.
As long as the valves are matched and as long as they
have equal duty, I can't see there being any real problems.
If you want to control them you could put them on solenoid valves
and then you could shut one down while you set the superheat
for the other and visa-versa.
If it is a cost thing then remember two smaller valves could be dearer
than one larger valve and be aware of space issues for fitting both in.
Rob
09-07-2013, 01:48 PM #5
Re: parallel TXV
I have seen it in split capacity systems, each valve opperates half a coil independant of each other, but with a common suction line. with only one fitted with a solenoid cut off valve, once room capacity is met and load stable they shut off one valve and the system is held by the master valve.
Now in Redvers Sask.
09-07-2013, 02:13 PM #6
Re: parallel TXV
It's mostly just an idea, although I did find some extra cheap 1/4 ton R22 TXVs and it would be nice if I could use two of them in my 1/2 ton air conditioner/dehumidifier. And if I add a solenoid to shut one of them off, I could possibly get more control range.
09-07-2013, 02:20 PM #7
Re: parallel TXV
remember, when you reduce load at coil you need to equaly unload compressor!
VFD's are pretty damned cheap now days, but beaware the oiling of the compressor.
to use them you need a vcp100 charge for the txv head, and you need to devide your coile in to 2 halfs equaly!Now in Redvers Sask.
09-07-2013, 10:36 PM #8
Re: parallel TXV
If you download document 10.9 from http://www.sporlanonline.com via the literature section and read page 11 you will see their take on the subject.