Results 1 to 8 of 8

Thread: parallel TXV

  1. #1
    Join Date
    Jul 2013
    Location
    USA
    Posts
    58
    Rep Power
    11

    parallel TXV



    Would it work to connect two TXVs in parallel and use them as one big TXV?



  2. #2
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: parallel TXV

    Yes it will work. By the way what is the application you are asking for ?

    Regards
    Sendhil

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: parallel TXV

    Quote Originally Posted by NiHaoMike View Post
    Would it work to connect two TXVs in parallel and use them as one big TXV?
    I think if 2 valves used they would fight each other. 1 larger valve would be better if you can get it big enough, if not there are ways around it.

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: parallel TXV

    .

    It would work if you fed them into a distributor.

    As long as the valves are matched and as long as they
    have equal duty, I can't see there being any real problems.

    If you want to control them you could put them on solenoid valves
    and then you could shut one down while you set the superheat
    for the other and visa-versa.

    If it is a cost thing then remember two smaller valves could be dearer
    than one larger valve and be aware of space issues for fitting both in.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: parallel TXV

    I have seen it in split capacity systems, each valve opperates half a coil independant of each other, but with a common suction line. with only one fitted with a solenoid cut off valve, once room capacity is met and load stable they shut off one valve and the system is held by the master valve.
    Now in Redvers Sask.

  6. #6
    Join Date
    Jul 2013
    Location
    USA
    Posts
    58
    Rep Power
    11

    Re: parallel TXV

    It's mostly just an idea, although I did find some extra cheap 1/4 ton R22 TXVs and it would be nice if I could use two of them in my 1/2 ton air conditioner/dehumidifier. And if I add a solenoid to shut one of them off, I could possibly get more control range.

  7. #7
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: parallel TXV

    remember, when you reduce load at coil you need to equaly unload compressor!

    VFD's are pretty damned cheap now days, but beaware the oiling of the compressor.

    to use them you need a vcp100 charge for the txv head, and you need to devide your coile in to 2 halfs equaly!
    Now in Redvers Sask.

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: parallel TXV

    If you download document 10.9 from http://www.sporlanonline.com via the literature section and read page 11 you will see their take on the subject.
    Last edited by Brian_UK; 09-07-2013 at 10:47 PM.
    Brian - Newton Abbot, Devon, UK