    heat pump capacity adjust



    one ground source heat pump for air handling:
    *ground side use plate heat exchanger
    *air side use fin coil heat exchanger
    *Summer day--fin coil as evaporator to dehumidify air ,condensing heat reject by ground side plate heat exchange
    * winter day--heating air by fin coil condensing heat

    The main concern is how to control condensing heat in winter by the most economic way. Air volume is required by customer and not allowed to adjust. Compressor is fixed volume. I'm not sure if the hot gas bypass can apply for this situation? or adjust underground side water flow?
    thx in advance

    rgds
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Wink Re: heat pump capacity adjust

    Danfoss have water regulating valve wich reduces water flow acording to the condensing temperature.

    Best regards,
    Renato

  3. #3
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: heat pump capacity adjust

    you're right. But the condenser is air cooled. The main concern is the air flow in summer is double the air flow in winter day and the condenser heat is more than the required for air heating in winter. In other word,the air flow is not enough to bring out the condenser heat and the condensing pressure will increase ,may cause the system can't work. The compressor is fixed displacement.How to keep the condensing pressure in normal range?

    rgds
    LC
    I hear...I forget;I see...I remember;I do...I understand

  4. #4
    Join Date
    Feb 2006
    Location
    WA, USA
    Posts
    62
    Rep Power
    19

    Re: heat pump capacity adjust

    Cycle the unit on discharge temperature in heating mode?
    Throw the extra heat somewhere else? (Duct bypass)
    Cycle the unit on a room thermostat?
    Will melt ice for $101/hr

  5. #5
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Question Re: heat pump capacity adjust

    Is it posible to increase volume flow but 1/2 the air take out by duct.So that volume of air stais as customer wants.

    Best regards,
    Renato

  6. #6
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: heat pump capacity adjust

    good questions
    Cycle the unit on discharge temperature in heating mode?
    if the dischange temp over the limit, of course, stop compressor. --it's needed by any refrigeration system
    Throw the extra heat somewhere else? (Duct bypass)
    it's a good way though it's not energy saving in some special situation.
    Cycle the unit on a room thermostat?
    I'll consider it because it relates to the HVAC system design issues.

    thanks

    regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

Similar Threads

  1. New Heat Pump Forum
    By Argus in forum Heat Pumps
    Replies: 17
    Last Post: 10-04-2010, 09:12 AM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. Attic Heat Pump
    By KETTLER in forum Heat Pumps
    Replies: 35
    Last Post: 23-02-2008, 11:33 PM
  4. Homemade Heat pump water heater
    By busman in forum Technical Discussions
    Replies: 20
    Last Post: 05-02-2008, 04:04 PM
  5. Rebuild air2air heat pump
    By stalker in forum Technical Speculations
    Replies: 3
    Last Post: 02-11-2006, 10:10 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •