    Hot and Cold Chamber rate of heating and cooling



    I am currently in the process of building a hot and cold humidity chamber Type -1
    Test space : 100 litres
    450 mm x 450 mm x450 mm
    -70 to +100


    The average rate of heating and cooloing required is 2.5k per minute.
    Can some one explain how do i figure that out in terms of temperature/min?



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Hot and Cold Chamber rate of heating and cooling

    K=Kelvin and for all intent and purpose (at least for your calculations) is the same as degrees C.