    As a PLC programmer I have been asked to write logic for a Grasso Compressor that does not have an oil pump. It does have a Pressure Control solenoid valve.
    Can anybody briefly explain how this type of oil system works and how to start the compressor and monitor the pressure ?
    I am more used to having an external oil pump which we start before the compressor and allow oil pressure to build up
    Jun 2011
    Australia
    44
    336
    21
    Re: Grasso Compressor Without Oil Pump
    Hi MP,
    Screw compressor with out oil pump is referred to as "differential fed" oil pressure.
    The compressor discharge pressure (or more correctly oil seperator pressure) pushes the oil from the seperator, through the oil filter, through the header & into the oil galleries.
    What needs to be measured (and controlled for safety) is oil manifold pressure (otherwise seperator pressure or discharge pressure, but manifold would be preferable) versus suction pressure. The difference between manifold pressure & suction pressure is referred to as "differential oil pressure".
    Obviously warnings, alarms & safeties need to be programmed for low differential pressure, usually with a time delay.
    Differential oil feed is usually only an option for single stage or high stage duty - not for booster / low stage duty.
    Also, best practice is to have a minimum pressure valve fitted on oil seperator outlet (aka discharge line). Upon start up when seperator pressure is low - the minimum pressure valve remains closed until the oil seperator builds up suitable pressure, then the min press valve opens - allowing passage of discharge gas for normal operation. Sometimes referred to as a cold start valve or various other names.
    Basic control sequence would be
    a) At rest i.e. zero differential pressure, allow compressor start but activate oil pressure timer
    Then
    b) compressor starts & oil differential pressure increases to above trip value - happy days - compressor is allowed to run unless oil pressure falls below trip value for delay time
    Or
    c) compressor starts & oil differential pressure does not increase above trip value within delay time - fail compressor on low differential oil pressure.
    Auckland
    74
    3,357
    37
    With out external pre-lube or continuous oil lube pump, the system relies on seeing a differential oil pressure driven by discharge pressure driving oil flow. A start instruction will rely on a pressure differential pressure from two transducers to continue. No or low prescribed oil diff pressure equals a fault condition, time delayed by seconds. BUT some grassos have internally driven oil pumps, and inboard oil filters. Just to confuse things. Same rules apply. Hope this helps.
    Jul 2011
    Australia
    5
    Thanks for the reply guys - can't get a clearer explanation than that !
    I also noticed from a photo of the compressor that it has 2 each load and unload solenoids. I have only ever come across one of each. Any reason for the two you know of ?
    Jun 2011
    Australia
    44
    336
    21
    Yep, the simple explanation is "Grasso have Two"
    Just the same otherwise, one PLC output for load and one for unload. Connect the two corresponding solenoids in parallel.
    3,362
    A oil float on oil separator is also important with protecting compressor. Which model do you have to be completely clear with advice?
    Aug 2007
    Adelaide Australia
    70
    562
    Hi MP
    Another few things to add into your program is if the compressor crash stops you have to energise the two unload solenoid valves as there is an internal spring which will push the slide to the unload position when the compressor is not running.
    The oil separator should have a level switch installed as a safety so you don't run out of oil because with differential feed machines you are relying on pressure only and you could have gas pressure in the manifold and not oil pressure.
    When the compressor is started you will have to load the compressor reasonably quickly to assist in getting the discharge pressure up as quickly as possible.
    Paul
    Jul 2011
    Australia
    5
    Thanks for the Info - Lots to take into account. RANGER1 unfortunately I don't have the model number at this time but I'll defo check on the Oil Level monitoring.
    Feb 2013
    Rochester, NY
    37
    I don't like the idea of dry-starting a machine until oil pressure builds up.
    Iceman717
    Compressors in the basement, condensers on the roof, evaporators everywhere else. :cool:
    3,362
    Quote Originally Posted by Iceman717 View Post
    Why if it has roller bearing cannot see the problem. Trick have a 15 min oil trip timer
    Jan 2006
    Croatia
    68
    2,261
    31
    Hi, MP231
    Quote Originally Posted by MP231 View Post
    welcome to RE forums ...
    I'm just curious ... is this some petrochemical plant ....
    Other guys gave you a very good advices, but still you have a lot to do to wrote a good logic ... hope all transmitters are installed within compressor ...
    ... with external oil pump and oil pressure by-pass valve things will be easier for you ...
    Best regards, Josip
    Jul 2011
    Australia
    5
    Hi Josip
    No its not petro chem just a simple chiller. Yes a lot of good advice and at the end of the day the mechanical guys will ensure it is running and stopping as it should. Nice to get as much of it as possible right beforehand though. Thanks.
    Feb 2013
    Rochester, NY
    37
    I don't know. I guess I'm just too used to machines with external pumps and needing to see a certain oil pressure before it will start. Spinning things without oil pressure gives me the willies.
    Tom
    3,362
    Tom
    Frick who I imagine dominate the USA market have been doing it for a considerable time, seem to handle differential oil pressure feed. Rollers with clean oil are pretty forgiving. A Frick engineer mentioned a new Frick was somehow piped up incorrectly & one roller ran for several months without fresh lube before failing (believe it or not). Even recipes run for up-to 90 secs without oil pressure before they cut out on oil trip. Like with a lot of things, a little lube goes a long way!
    ireland
    54
    275
    26
    We used to use small bitzer screws like this,they used to have a float switch on the seperator/ resevoir,an oil flow switch on the oil line connected into the int thermister box,there was also a heater on the resevoir controlled by a stat to keep the oil temp up in downtime.There was also a solenoid on the oil line to stop the oil migrating and locking the rotors when the machine was off.
Tags for this Thread