Ive been asked to add a condensate pump to a daikin atx35j2v1b wall mounted unit.
Can anyone please confirm which terminals are live and neutral as ive confused myself with the wiring diagram.
-
03-07-2013, 07:05 PM #2
Re: Daikin atx35j2v1b wiring question
1 live 2 neutral 3 pulsed signal- dont connect anything like hi limit through signal wire
some siesta units use 5 core interconnect-
service manual for reference
click on blue link
http://www.mediafire.com/download/29...219-286230.pdfLast edited by install monkey; 03-07-2013 at 07:25 PM.
-
03-07-2013, 07:31 PM #3
Re: Daikin atx35j2v1b wiring question
Thank you so much for a quick reply. I thought it was but then talked myself out of it when i saw a red connection on 3.
Im sure i will have many new-by questions in the next few months.
-
03-07-2013, 07:37 PM #4
Re: Daikin atx35j2v1b wiring question
Can you please tell me where i can download all of those manuals, ideally for daikin, mitsubishi and fujitsu??
-
03-07-2013, 10:31 PM #5
Re: Daikin atx35j2v1b wiring question
Try the manufacturers websites