    407C Pressures and Temps



    Just had a a Baily unit with a 7.5HP compressor changed over to 407C. This has a seawater cooled condenser. I was looing for help regarding operating temps and pressures. I am finding that the suction pressure is remaining low (42PSI) and the high side around (240). It appears the system has the proper charge and is cooling the space.

    Any help to put me the the right direction would be greatly appreciated.

    Regards,



  2. #2
    Join Date
    Jun 2008
    Location
    NZ
    Posts
    102
    Rep Power
    17

    Re: 407C Pressures and Temps

    What are your Air on/Air off temps?

    What is your EWT and LWT?

    Does the system have a fixed expansion device, or a TEV?

  3. #3
    Join Date
    Jun 2013
    Location
    USA
    Posts
    2
    Rep Power
    0

    Re: 407C Pressures and Temps

    Thank you for the response.

    Air On and Air Off refers to in and out of the coil? If so it is 80F and 65F.

    The EWT is 85F and the LWT is 96F.

    A TXV has replaced a capillary tube device.

  4. #4
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: 407C Pressures and Temps

    The high side pressure seems ok for the water cooled condenser. May need to vrify the TXV capacity at this condition w.r.t compressor capacity. What is the super heat ?

    Regards,
    sendhil