    Exclamation Daikin Euwa



    Dear all

    I`m looking for service documentation for Daikin chiller Daikin EUWA100HASDY1 1998 380047. ( two compressors) One of compressor is starting operation and stops after 0.5 seconds. Unit was switched off for 3 months. Range of outside temperature during iddle state -25 : - 10 deg C. I checked amount of refrigerant -OK. The controller after shutting off the compressor indicate alarm led without any description also compressor motor protection is off. . No idea if oil can migrate from compressor ( heater was on during mentioned 3 months). Is it possible that having documentation i can check in the control panel what is the reason of failure. ???

    Thanks for help
    Best regards.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Euwa

    I've got the info at the office. I'll post the error codes tomorrow

  3. #3
    Join Date
    Feb 2006
    Location
    Poland
    Posts
    5
    Rep Power
    0

    Re: Daikin Euwa

    It will be great if you can send me any information. I cant find anything in my country because the unit wasnt bought by factory from Daikin in Poland but was imported as second hand from abroad. That is the reason nobody hear about this model before in our regional offices.
    I chcecked the controller but it needs a password. The company which installed the unit,does not exist. Nobody knows password. I ve read manual from similar model EUWA MZSDY The standar password is 1234 but in my controller there are not buttons with digit, only arrows + and - enter key etc.
    If you can sent me any information it will be fine. If it impossible because of the size in MB you can send me this via post office ang charge me.
    Best regards

  4. #4
    Join Date
    Sep 2005
    Location
    Granard, Ireland
    Age
    55
    Posts
    43
    Rep Power
    0

    Re: Daikin Euwa

    Rysiozklanu
    Will the second compressor start and run?
    Check voltage.
    I will have a look for a pdf manual i have some place.
    regards

  5. #5
    Join Date
    Feb 2006
    Location
    Poland
    Posts
    5
    Rep Power
    0

    Re: Daikin Euwa

    The first compressor runs without any problem. The second runs 2 - 3 seconds. I have not enough time to diagnose it.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Euwa

    Fault Codes

    A1 Anti-freeze alarm
    E1 Evap Inlet water temp NTC Probe defective
    E2 Evap Outlet water temp NTC Probe defective
    E3 Evap heater tape fuse blown or reverse phase error or PCB error
    EE, EP EEprom defective
    EU, EO Supply voltage low (EU) or exceedingly high (EO)
    EL Power supply is excessively noisey
    FL Low water flow or pump overload activated
    H1 High Pressure switch activated
    L1 Low pressure switch activated

    if FL and H1 flash alternately then you have a reverse phase problem

    n1 Indicates that compressor 1 requires routine maintenance

    n2 Indicates that compressor 2 requires routine maintenance

    Press the SEL key for 5 seconds to adjust the parameters

    r1 cooling temp setpoint
    r2 colling temp differential
    r6 check evap water outlet temp
    c9 check total running hours of comp 1
    cA check total running hours of comp 2
    cC check total running hours of pump

    The password is 22 - Factory default

    Press PRG key for 5 seconds
    number 00 starts flashing
    Enter 22 using the up/down arrows
    Press SEL key to confirm
    the controller then displays rd which is the first parameter.

    Let me know if you need the parameter list (it's rather long)

  7. #7
    Join Date
    Feb 2006
    Location
    Poland
    Posts
    5
    Rep Power
    0

    Re: Daikin Euwa

    I get the documentation somehow. Your codes are different than in mentioned chiller ( probably units are provided with different controllers depending on the country) I found the problem - discharge temperature sensor faulty. Any way Thanks for codes.
    Best regards from Poland.

  8. #8
    DarkRain's Avatar
    DarkRain Guest

    Re: Daikin Euwa

    Hello..

    I have this error
    L1 Low pressure switch activated

    how can i repair this ? please help me.

  9. #9
    Join Date
    Aug 2008
    Location
    London
    Age
    42
    Posts
    55
    Rep Power
    16

    Re: Daikin Euwa

    Quote Originally Posted by frank View Post
    Fault Codes

    A1 Anti-freeze alarm
    E1 Evap Inlet water temp NTC Probe defective
    E2 Evap Outlet water temp NTC Probe defective
    E3 Evap heater tape fuse blown or reverse phase error or PCB error
    EE, EP EEprom defective
    EU, EO Supply voltage low (EU) or exceedingly high (EO)
    EL Power supply is excessively noisey
    FL Low water flow or pump overload activated
    H1 High Pressure switch activated
    L1 Low pressure switch activated

    if FL and H1 flash alternately then you have a reverse phase problem

    n1 Indicates that compressor 1 requires routine maintenance

    n2 Indicates that compressor 2 requires routine maintenance

    Press the SEL key for 5 seconds to adjust the parameters

    r1 cooling temp setpoint
    r2 colling temp differential
    r6 check evap water outlet temp
    c9 check total running hours of comp 1
    cA check total running hours of comp 2
    cC check total running hours of pump

    The password is 22 - Factory default

    Press PRG key for 5 seconds
    number 00 starts flashing
    Enter 22 using the up/down arrows
    Press SEL key to confirm
    the controller then displays rd which is the first parameter.

    Let me know if you need the parameter list (it's rather long)
    Hi Frank - Do you have any wiring diagrams or know about the controller functionality?

    many thanks for your input

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Euwa

    Same question asked via PM - answer given via PM

Similar Threads

  1. Daikin VRV Checker
    By bobjob in forum Air Conditioning
    Replies: 6
    Last Post: 04-01-2009, 08:10 PM
  2. Daikin Analyzer
    By marc5180 in forum Fundamentals
    Replies: 10
    Last Post: 02-08-2008, 07:15 PM
  3. Daikin Controllers
    By airefresco in forum Air Conditioning
    Replies: 5
    Last Post: 15-05-2008, 08:08 AM
  4. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM
  5. Daikin Model
    By Geofridgee in forum Air Conditioning
    Replies: 1
    Last Post: 12-07-2006, 09:23 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •