Results 1 to 8 of 8
  1. #1
    Join Date
    Jun 2012
    Location
    Dubai
    Age
    36
    Posts
    2
    Rep Power
    0

    Piping for a compressor pack having multiple evaporators.



    Hi,

    I would like to know about the piping guide line for compressor pack serving multiple evaporators having different capacity.

    I want to know how the branches of the main lines are done; is it as per the capacity of the evaporators.


    Thanks in advance



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Piping for a compressor pack having multiple evaporators.

    Have a read of some of the information available from the Sporlan literature store....
    http://sporlanonline.com/literature-...nal-materials/

    A good layout diagram is under the misc section and document 5-180.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2012
    Location
    Dubai
    Age
    36
    Posts
    2
    Rep Power
    0

    Re: Piping for a compressor pack having multiple evaporators.

    Dear Brain,

    Thanks for the input. But i am looking for a guide line for" pipe sizing" a refrigeration system with one compressor rack ( 3 x 30hp) serving 4 coolers.

    regards,
    Christopher

  4. #4
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    20

    Re: Piping for a compressor pack having multiple evaporators.


  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Piping for a compressor pack having multiple evaporators.

    they need to increase the size limmit for pdf's, I have the exact thing you want but allas it is 4 meg pdf.
    Now in Redvers Sask.

  6. #6
    Join Date
    Sep 2011
    Location
    USA
    Age
    45
    Posts
    84
    Rep Power
    14

    Re: Piping for a compressor pack having multiple evaporators.

    Download the Sporlan selection software or contact Sporlan rep to get it. There is all kinds of line sizing capability on this. I use this for all of my line sizing.

  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Piping for a compressor pack having multiple evaporators.

    Hi, Chris ref

    Quote Originally Posted by Chris ref View Post
    Dear Brain,

    Thanks for the input. But i am looking for a guide line for" pipe sizing" a refrigeration system with one compressor rack ( 3 x 30hp) serving 4 coolers.

    regards,
    Christopher
    You can download Danfoss DIRCalc ... there you can calculate pipe sizes for your system with dry, pump or gravity feeding with relevant refrigerant etc. ....

    ftp://software.danfoss.com/RA/DirCalc/DirCalc.zip

    .... you calculate pipe size for each branch as per size of evaporator .... as you connect two branches then the header became bigger after third is again bigger and then after fourth branch I think is the final size of the common header ... I assume your compressor rack must work with max two compressor in the same time and the third one is a stand by compressor ... so try to check the last portion of your header for 60HP ...

    take care about pipe slopes and connections with siphons to get oil back to compressors ... as per suggestion of other members it will be good to read some manuals for piping layout ...

    Hope this will help a little ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Piping for a compressor pack having multiple evaporators.

    Or the Bitzer website has some interesting guidelines
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Posting Permissions