Thread: Error code P6 on Midea VRF
29-06-2013, 05:11 AM #1
Can anyone help me determine the cause or problem of error code P6 ( Inverter module protection )? The model is Midea SA-MDV-V450W/N1. Condenser fan runs for a few minutes and stop while the compressor never runs at all. Then after another few minutes fan motor will start and stop again. Maybe this will help, I was informed that the compressor was already replaced. When I checked the condenser, I also saw signs of leak repair at one of the pressure sensor.
29-06-2013, 09:46 AM #2
Re: Error code P6 on Midea VRF
ive searched my manuals and i dont have any vrf ones but on other models p6 is referring to hp trip on system A
30-06-2013, 04:31 AM #3
Thanks for the quick reply. However, the description on the error code table of this unit is inverter module protection.
30-06-2013, 05:07 PM #4
http://yadi.sk/d/Au9BJsb56LGYq
this will help you a little.
http://yadi.sk/d/boxUOehv6LHIQ
http://yadi.sk/d/9VKzAHMg6LHNm
Its all for D3, and and does not include D4v+Last edited by RusBuka; 30-06-2013 at 05:12 PM.
01-07-2013, 02:14 PM #5
Thank you very much RusBuka. I think this will help me a lot.
26-07-2013, 06:27 AM #6
I tried to switch the PC board from other units and the result is an error code E0 ( communication error between outdoor units ). Is this mean the problem is PC board?
13-08-2013, 07:05 AM #7
It could be that the addressing is different on the PC board you put in, giving you an E0. It is possible that the inverter PCB has been damaged. P6 has a multitude of items that you need to check. It is a fairly common problem here in South Africa because of our unreliable power. Items that need to be checked include the contactor coil, the reactor, the IPM PCB, the power filter pcb or even the direction the "N" cable is going through the CT from the rectifier to the IPM PCB. I have attached a link to the troubleshooting manual. https://dl.dropboxusercontent.com/u/...troduction.ppt