19-06-2013, 04:29 PM #1
expansion valve body getting ice frozt
Hi
We having bitzer chiller for - 30 deg , in this chiller we are not able to go beyond -15 deg c also the expansion valve body getting ice frosting very frequently
Pl help me
Sekar
-
19-06-2013, 05:42 PM #2
Re: expansion valve body getting ice frozt
Sounds short of refrigerant.
-
20-06-2013, 05:27 PM #3
Re: expansion valve body getting ice frozt
Thank you for your information
-
10-07-2013, 02:32 PM #4
Re: expansion valve body getting ice frozt
Hold it that is a poor statement with out more data! never NEVER NEVER assume low refrigerent right away! bad practice!, what is the sub cooling on the txv and the Super heat, air in and air off condenser, only after we analyze the system can we question the gas charge!
Now in Redvers Sask.
-
10-07-2013, 06:45 PM #5
Re: expansion valve body getting ice frozt
It is not a poor statement at all it is a fact that frost on the body of a tev is a symptom of short of refrigerant I agree with a previous post of yours saying its not always gas but symptoms are how we find faults until further information is provided there is nothing else to go on.
-
Re: expansion valve body getting ice frozt
sensek75,
A little light reading.
http://www.emersonclimate.com/Docume...re-article.pdf
-
Re: expansion valve body getting ice frozt
Sekar,
What's the temperature of the space that the TXV is in? I'm sure it is above 0c, seeing as it is a chiller and not an air coil. The refrigerant is well below 0c (freezing). So if that's the case, the frost that you are seeing is nothing more than the water vapor from the surrounding air freezing to the outside of the valve.
Correct me if I'm wrong.
As for not being able to get below -15c, is it possible that you have too much load on the chiller? Is the flow rate correct?
-
11-07-2013, 07:44 PM #8
Re: expansion valve body getting ice frozt
I would say the ice build up on the tev must be abnormal for him to notice it and that on top of the struggling to reach temp would point me in the direction of a short of refrigerant diagnosis, obviously this is different to actually seeing the equipment so can only go off his symptoms.