    Double door Freezer temp issues



    Hi,

    I had been trouble shooting a 6 ft upright standing double door freezer at a Thai restaurant. The Carel controller is set to -19 and it can only achieve -10 degrees at its best.

    Previous techs have swapped the compressor, fitted new evap fans and to no improvement.

    Ive checked:

    Evap fans (x4) are all operations
    Evaporator and condenser coils are clean/clear
    Checked suction pressure at compressor and getting 20psig/-25 on R404A...

    The system has a CPR valve and the press. before the valve is about 20psig ... then it goes up to 40 psig (-10) at intervals... then drops... back to 20psig... all the while the suction line does not feel very cold at all in a freeze cycle and only frosts over during hot gas defrost (indicating the CPR valve is doing its job?)

    The lowest we have achieved is -14 and cannot get the desired -19 set point. The system is on capillary expansion, so should that signal alarm bells when theres a CPR valve fitted?

    Your advice would be greatly received.

    C



  2. #2
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: Double door Freezer temp issues

    Freezing back when it's on hot gas operation ring alarm bells, I would look at the gas charge as if its not cooling properly down the suction and the comp is ok sounds like it could be short. Does the drier feel warm/cold/hot?

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Double door Freezer temp issues

    .

    If you are confident that it is correctly charged with the right refrigerant,
    I would look at the back pressure regulator.

    If it fluctuates, it could be holding the evap temperature too high.

    Try opening the valve fully so the system runs at the lowest back pressure
    and see if it runs ok?

    The only other thing I would look at, would be the gas itself. Was the refrigerant
    replaced for new when the comp was replaced? How long ago was the compressor
    replaced? and has the condenser fan ever failed or the condenser blocked?

    It is possible for 404a to burn out (degrade through over temperature) due to blocked
    condensers or faulty condenser fans, but if you are confident the refrigerant is good and
    you are confident there is the correct charge, I would look to the comp or back pressure regulator.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..