    R290 + HC's



    Never dealt with the care range of refrigerants, looks like we will be dealing with small amounts. Gonna look at the BOC course...

    Main difference in procedure as opposed to our beloved normal refrigerants

    All input appreciated



  2. #2
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: R290 + HC's

    Been doing r290 and r600 for a bit now, main thing is weighing back in or buying really accurate gauges due to low pressures. From what we were told in f-gas course up to 150g is allowed to be released safely and foster have started putting majority of cabinets with a max of 150g.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: R290 + HC's

    First thing is to get yourself a combustible gas leak detector from a plumbers merchant.

    No smoking etc., a good purge out with N2 prior to any brazing.

    No loose electrical bits either.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: R290 + HC's

    Deal with it as you would when using petrol or BBQ gas, as that is what you are dealing with, just much cleaner and drier!

    Ensure your equipment is in good sound leak free shape, purge well with N2, and keep a clean job site, and keep fire extinguisher at hands reach (We all should have this any ways)

  5. #5
    Join Date
    Feb 2006
    Location
    England
    Posts
    64
    Rep Power
    19

    Re: R290 + HC's

    Hi, would anyone know if there is anyone could deal with calls on R290 in the Northampton/Leicester area ? (small stuff)

  6. #6
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: R290 + HC's

    Quote Originally Posted by jdunc2301 View Post
    Never dealt with the care range of refrigerants, looks like we will be dealing with small amounts. Gonna look at the BOC course...

    Main difference in procedure as opposed to our beloved normal refrigerants

    All input appreciated

    The course lasts about half a day and covers all the safety
    aspects to do with HC's.

    The main safety fact you will learn is the Lower flammability level
    and the practical limit, which are the levels of concentrations
    of the stuff in a room before it becomes flammable.

    Unbrazeing components could cause problems so there is a procedure
    to follow that reduces the risk of fire to almost nil.

    I actually set fire to the gas that vents through the gauges
    when I demonstrate the procedure, just to show how safe the
    stuff is.

    Do the course and don't worry, it is just a refrigerant at the
    end of the day.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  7. #7
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: R290 + HC's

    Quote Originally Posted by Rob White View Post
    The course lasts about half a day and covers all the safety
    aspects to do with HC's.

    The main safety fact you will learn is the Lower flammability level
    and the practical limit, which are the levels of concentrations
    of the stuff in a room before it becomes flammable.

    Unbrazeing components could cause problems so there is a procedure
    to follow that reduces the risk of fire to almost nil.

    I actually set fire to the gas that vents through the gauges
    when I demonstrate the procedure, just to show how safe the
    stuff is.

    Do the course and don't worry, it is just a refrigerant at the
    end of the day.

    Regards

    Rob

    .
    Good course! Cheers for today! Rep points will be added when i'm allowed to spread them out again!

  8. #8
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: R290 + HC's

    Starting to have doubts about the safety of hcs, coming across more and more stories of exploding fridges on the web and these are only domestics with 40 to 60 gram charge.Problem seems to be leaking joints behind the insulation leaking into the box at night when the concentration can reach the flammibility level.The damage in one of the photos was quite severe.

  9. #9
    Join Date
    Jul 2013
    Location
    USA
    Posts
    58
    Rep Power
    11

    Re: R290 + HC's

    Require all controls to be sealed or solid state. The whole problem is no different to the use of highly flammable lithium batteries in consumer electronics.

  10. #10
    Join Date
    Mar 2008
    Location
    uk
    Posts
    24
    Rep Power
    0

    Re: R290 + HC's

    Quote Originally Posted by 1mikeefc1 View Post
    Been doing r290 and r600 for a bit now, main thing is weighing back in or buying really accurate gauges due to low pressures. From what we were told in f-gas course up to 150g is allowed to unt be released safely and foster have started putting majority of cabinets with a max of 150g.
    up to 150 gr lets put that on side for re-forum....its safe to released as long mix air(CONTAIN OXYGEN) and our hydrocarbon wont become flameable mix ...we are talking about closed spaces...when outside story is slightly diferent...
    cooled things come to those who wait...