    I have a display fridge that is continuously cooling beyond the set point of 7C.
    It has a Carel easy cool temperature controller.
    I have fitted a new NTC probe but has made no difference.
    Any ideas?
    Oct 2007
    manchester
    5,639
    45
    Re: Display fridge continuously cooling
    relay on controller welded/sticking- when its below sepoint tap it with ur fingers see if the relay drops out
    3,856
    What Monkey said^ Stuck relay, alter the set point to see if the compressor running indication dot on the display cycles to see for sure.
    I have once seen burnt wiring causing things not to turn off as the insulation had melted and the copper wire were touching.
    Dec 2010
    devon
    837
    with easy cools they also have a run time on them if set up could be running on time not temp also some have overun facility or ofset been set up incorrectley i no but it is a carel check to sea if snowflake is lit up on controller if no snowflake and its still cooling as above says i always used to fit just controller but now in last three years we fit relays to take load of controllers
    Jun 2013
    4
    Thanks will check the above.
    Link that shows parameter settings:
    http://www.carel.com/carelcom/web/do.../050004121.pdf
    Jun 2013
    4
    Hi - tried the above suggestions.
    In the end fitted a new controller and it sorted the problem.
    I was holding the controller as I powered up the fridge and felt a distinctive click which I'm presuming is the relay energising on.
    Will use this site again.
    I bought the controller from Hawco - but they charged me £15 for delivery! Does any body know anywhere cheaper?
    Oct 2007
    manchester
    5,639
    45
    srw do em-dunno how much
    sometimes theres a relay on a pcb that switches a higher rated relay
    3,856
    I expect the cost of postage has to to cover the packaging/postage and the persons wages who picks and packs the items.
    I had to post a part to a customer, the postage was £5.50 but taking into account the time it took and my normal hourly rate it should have cost them nearly £60.00 for a part i made £4.20 mark up on....
    Now Hawco will be much better set up for sending stuff than me but it will have a cost.
    Oct 2007
    manchester
    5,639
    45
    dunno john, bet your origami/ninja training ensures all folds are sharp and crisp and bet ur a dab hand with the bow!