    hi,i am a student.In my final project,i had to design a small system of refrigeration system.Now i have a problem to calculate the length of evapurator.Have anyone can help me this this problem??

    I really have no idea to find out how long the evapurator i need.
    Or someone who can introduce me the book regarding to my problem.



  2. #2
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26

    Sizing an evaporator

    hello heanboon,

    I have a suggestion. Approach a local refrigeration spares company and ask them to select both a condensing unit and evaporator for you based on the size of the refrigeration space you are using together with the desired temperature.

    They will arrive at a duty , either in BTU's or Kwatts, watts, whatever.

    The "size" of the evaporator is measured in watts and is matched against the duty of the compressor.

    In a nutshell, you achieve a balance of the two. As an aside, you need a lot of experience and brains to work it out scientifically. And you need to embark on a PHd if you want to work it outself. Dont even try.

    And if youre designing a system, then you would, or should know all this stuff already!!

    Dunno, maybe other members can be more constructive then I have been

    Good luck
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  3. #3
    Join Date
    Apr 2001
    Location
    Southern England
    Age
    66
    Posts
    123
    Rep Power
    23

    Cool Evaporators - What For?

    Work with us on this one..


    Are you looking at air cooling or fluid cooling?

    Is this a domestic size application e.g. you don't want a fan to increase the heat transfer rate.

    Are you working at high (ambient) temperatures or are you in the frozen zone.

    I guess you are looking at a small air cooled unit in which case you have several local suppliers making Searle, Kuba and Friga Bohn copies. For a really small unit you will be looking at a flat plate normally sold as a repair item or in 1000's off.

    Evaporator capacity is rated as Q=AxUxTD

    Heat transfer in watts = surface area (including fins) x conductance figure x log mean temperature difference external temp to refrigerant temp.

    Work with this and you will end up with an evaporator far larger than you need. I know I tried and Aiyub is 101% correct designing from scratch ain't practical.

    Try R J Dossart -Principles of Refrigeration

    and for the PhD D's amongst you;

    Webb - Principles of Enhanced Heat Transfer

    www.searle.com will give you spec selection data on evaporators and fin coil selection data.

    I'd also recommend SWEP for liquid / liquid heat exchangers on www.swep.se
    'cause they just helped me out the mucky stuff with some failed Scandinavian stuff.

    Go on give us the duty and more info and we will have a go.
    Derek

Similar Threads

  1. Howto: Calculate coaxial heat exchangers
    By JKProSoft in forum Technical Speculations
    Replies: 14
    Last Post: 10-01-2011, 01:10 PM
  2. How to calculate enthalpy?
    By thing in forum Refrigerants
    Replies: 5
    Last Post: 29-10-2005, 03:10 PM
  3. Help to calculate Heat Exchancger
    By Carode in forum Fundamentals
    Replies: 1
    Last Post: 17-12-2003, 11:57 PM
  4. Calculate cap tube
    By herefishy in forum Technical Discussions
    Replies: 55
    Last Post: 04-11-2003, 09:31 PM
  5. How do you calculate Superheat?
    By zolar1 in forum Training
    Replies: 39
    Last Post: 10-05-2002, 02:37 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •