Results 1 to 9 of 9
    Jul 2011
    usa
    29
    three terminal start relay
    Ok, my brain is melting on this one.
    I swapped a compressor (aea3425yxa, 1/5hp) for a new compressor. Same techumseh model number, but they were out. However, they did some searching and I got the same compressor, rebadged under a manitowok part number. New compressor still shows aea3425yxa.
    Difference is in the start relay. The new start relay has two terminals for the compressor (m and s) and only one other terminal. I'm used to four terminal relays, m, s, and a place to put line voltage and another to attach the start capacitor.
    The tech sheet from tecumseh specifies that it should be used with a start capacitor. I'm very hesitant to hook up the old start relay because the compressor is a burnout and I haven't excluded the start relay.
    So, any hints on how to hook up a start relay with only one terminal (aside from the compressor hook-up) ? Is this a wrong part, meant for some compressor that doesn't require a start capacitor?
    I have been reading schematics in my refrigeration bible, and haven't found a thing.
    Old relay on left new one on right.
    Any pointers would be greatly appreciated.
    Thanks!
    Oct 2007
    manchester
    44
    5,707
    Re: three terminal start relay
    http://www.mediafire.com/download/96...aea3425yxa.pdf
    its a LST comp-low starting torque
    no capacitor needed on that compressor- its a rsir comp just live to the relay and neutral to the overload.
    best check with the manufacturer of the unit to see if a med/high start torque compressor is needed
    Jul 2011
    usa
    29
    The tecumseh esp guidebook lists it as requiring a capacitor.
    Thank you.
    Do these guys often change the specifications on a compressor and reuse the model number?
    Oct 2007
    manchester
    44
    5,707
    http://www.mediafire.com/download/oo...CUMSEH-002.pdf
    info on dataplates on compressors
    Jul 2011
    usa
    29
    Interestingly enough, their nomenclature doesn't specify low starting torque anywhere in that pdf. It only shows normal and high starting torque.
    Oct 2007
    manchester
    44
    5,707
    AE170AL-726-J7 AEA3425AXA 115-60-1 R-12 1/5 2600 Normal * P82627‡ P83458 1/4 S 5/16 S LP3
    didnt copy too well- it states the part numbers for the relay and klixon overload and refers to it as normal starting
    Jul 2011
    usa
    29
    "Normal starting" is "low start torque" i.e. no capacitor?
    Jul 2011
    usa
    29
    Also, perhaps I'm reading this wrong... this is from Tecumseh's android app.
    Oct 2007
    manchester
    44
    5,707
    http://www.tecumseh.com/en/europe/contact-us
    looks like ur ringing technical to clarify
    some compressors can have caps fitted as an option but the relay would need 2 connections to bridge it