    Water Sweating from HRW unit



    Hi friends...
    Recently we had installed the HRW ( Heat Recovery Wheel ) for OT.mine problem is that, outside the unit water is sweating, for this i have attached the pics also.i was unable to find the right

    Photo0161.jpg
    solution for it.what may be the problem..? any suggestions..



  2. #2
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Water Sweating from HRW unit

    LOL are you using it as a supply pre-cooler! What are your outside air conditions? What are the exhaust air conditions? measure these two conditions and post them here for explanation.
    Last edited by hookster; 15-06-2013 at 07:08 PM. Reason: addition
    I love the smell of Ammonia in the morning!

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Water Sweating from HRW unit

    Anil,
    To answer your questions,
    It is happening because the exposed surfaces are at a temperature below the dew point of the surrounding air and the solution is to lag (=insulate) it better.

    The bigger question is what is causing the surfaces to be that cold in the first place and here I agree with Hookster, we do need more information.
    It would be interesting to know both humidity and temperatures of the ambient, supply and extract air.



    .

  4. #4
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: Water Sweating from HRW unit

    @hookster and Viking: below is the details of it: 1) Intake Flow CFM.................1124.5 2) Intake frequency ................55 Hz 3) Exhaust frequency...............35 Hz 4) Delta p ( Pa )......................3 5) Air Velocity.............Min.....0.22 Max.....0.48 ......0.376 6) Noise........Ambient ..........22.5 db with Ac............50.5 db i hope, i have given all the information...

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Water Sweating from HRW unit

    Lots of information there Anil, sadly none of which we need to help you with this issue.

    What we do need is real life measured temperatures and humidities.

    Sorry


  6. #6
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Water Sweating from HRW unit

    Hi Anil as per Viking request its temp/RH issues you have here. I am expecting very high humidity on the exhaust due to the nature of mining conditions. If you like look at this http://en.wikipedia.org/wiki/Thermal_wheel it will probably answer your questions.
    I love the smell of Ammonia in the morning!