    Mitsubishi system not cooling



    Hi guys
    i am back to site , Monday with the replacement G50-A control . I've seen the guy from the office where it's to be fitted. He's just told be that half the 3rd floor is not cooling now . With no faults shown , don't think it's any thing to do with the G50-A, as when it stopped every thing would not run , has any one got any points to look at first . This new job is a job I wish we didn't get so many things going wrong
    Last edited by Paul a/c; 15-06-2013 at 07:09 PM.



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Mitsubishi system not cooling

    Start by looking at the system that serves the area concerned, if need be disconnect it from the G50 and run it as a stand alone system.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: Mitsubishi system not cooling

    Ok thanks will check that b4 I change the G50-A. Was thinking it could be lp or valve in bc boxing not opening

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi system not cooling

    check basics first, dirty filters, fault codes,power ok
    http://www.mediafire.com/folder/4hkq...i_tech_cd_2011
    mitsi 2011 toolbox

  5. #5
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: Mitsubishi system not cooling

    Yup Paul, I also agree with you that nothing to do with new G-50A. But make sure to check again your registration of groupings, settings/scheduling, date, time and etc. Any individual remote?

  6. #6
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: Mitsubishi system not cooling

    The installers have gone bust company closed down . The G50 -A has not come in some time this week they say , when it comes down il have to find the right VFV outdoor and see how that's running. Hope it's not big fault to go into ,
    thanks for the pointers , will let you guys know when I go back to site . JoeAT50A on site there's two G50-A one for ground and first and other for 2nd and 3rd . The hole system is run of a few P C around the office a T200-ta system .
    Last edited by Paul a/c; 17-06-2013 at 12:16 PM.

  7. #7
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Mitsubishi system not cooling

    Quote Originally Posted by Paul a/c View Post
    Hi guys
    i am back to site , Monday with the replacement G50-A control . I've seen the guy from the office where it's to be fitted. He's just told be that half the 3rd floor is not cooling now . With no faults shown , don't think it's any thing to do with the G50-A, as when it stopped every thing would not run , has any one got any points to look at first . This new job is a job I wish we didn't get so many things going wrong
    1. Did it work previous to you installing G-50? 2. Are there local controllers for this system? 3. Do you know the addressing of this system, indoor, outdoor, BC and remotes? are these addresses seen by the G-50?

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi system not cooling

    with tg2000 you can see history of all sensors on the system, return air,coil temp- give u an idea if anything is wrong. indoor spurs switched off will not generate a fault
    Quote Originally Posted by Paul a/c View Post
    The installers have gone bust company closed down . The G50 -A has not come in some time this week they say , when it comes down il have to find the right VFV outdoor and see how that's running. Hope it's not big fault to go into ,
    thanks for the pointers , will let you guys know when I go back to site . JoeAT50A on site there's two G50-A one for ground and first and other for 2nd and 3rd . The hole system is run of a few P C around the office a T200-ta system .

  9. #9
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: Mitsubishi system not cooling

    The new G50-A has not come down still waiting . Got the old one up and running again by powering down , didn't want to touch it again , once new one comes in il fit that and see what happens.

  10. #10
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: Mitsubishi system not cooling

    I'd check the capacity of outdoor against the indoors have came across this before ,youll get company's installing the wrong equipment just to cut costs and get the job.

  11. #11
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: Mitsubishi system not cooling

    Hi guys thanks for the help . Been to site today as people are phoning up saying there to hot , and just been told by Mitsubishi that the G50-A are no longer made , had to get all unit info , found out door unit for area was not running , opened up had : on the outdoor pcb powered down and up again all come back in and started cooling . Lets hope it stays like that . As we find out about the replacement for the G50-A control .

  12. #12
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: Mitsubishi system not cooling

    Hi Paul, there is an another option to replace. Model named GB-50ADA (without LCD). Since you have TG2000A PC, they seldom used G-50A screen for sure. It's cheaper I believed.

  13. #13
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: Mitsubishi system not cooling

    Thanks il have a look into this and see what they want to do