    Jun 2008
    india
    11
    York chiller loading issue
    HI,
    the york chiller of the
    Model: YEWS170SAD we installed in our plant, at the time of starting % of loading increased up to 88 and motor is taking 160Amps, but in running even the temperature of the evaporator is increased also the % of loading not going beyond 60 % becos of this we couldn't maintain the chilled water system. pl can you help somebody
    Sekar
    Oct 2008
    mallorca, spain,
    75
    768
    Re: York chiller loading issue
    hi sekar,
    can you tell me who commissioned the chiller ?= sedgy
    Jun 2008
    india
    11
    hi
    The system commissioned by service provider of york
    hookster's Avatar
    Apr 2007
    Hampshire
    438
    32
    It would be worth checking to make sure you have a temperature differential across the evaporator.
    Check flow and pump direction. Some system parameters would be usefull.
    Jun 2008
    india
    11
    The evaporator temperature difference is 8 - 9 deg and we maintain the working pressure of chilled water system is 2 - 3 bar pressure
    rated pump flow is 115 m3 /hr but we didn't measure the actual flow
    hookster's Avatar
    Apr 2007
    Hampshire
    438
    32
    Hi sensek do you have the system set points and pressure/temperatures? Can you explain your plant requirements too? sorry for all questions but to diagnose faults from a distance all the information you can supply makes it more achievable.
    Apr 2009
    israel
    778
    pls state your actual temp differntial accros the evaporator ,
    has the system been limited by york not to load over 60%?
    you have a paramter to check this !
    stating system refrigerant pressures could be helpful to.
    good luck
    4,697
    Hi sensek.
    I don't know about your model of York chiller, maybe someone from York has heard if it?
    Anyway that's immaterial, any make of chiller with a half decent controller would unload or restrict the load capacity with a 6 to 8c temperature across it.
    Pump pressure is irrelevant, it's the pressure diff across the evap.
    You don't tell us how old this chiller is?
    Or how long you have had the issue?
    If you can measure the flow (as asked for by the above) then I suspect all will become clear.
    Most makes of chiller you would expect 3-4c diff fully loaded.