    York chiller loading issue



    HI,
    the york chiller of the
    Model: YEWS170SAD we installed in our plant, at the time of starting % of loading increased up to 88 and motor is taking 160Amps, but in running even the temperature of the evaporator is increased also the % of loading not going beyond 60 % becos of this we couldn't maintain the chilled water system. pl can you help somebody


    Thanks

    Sekar




  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: York chiller loading issue

    hi sekar,
    can you tell me who commissioned the chiller ?= sedgy

  3. #3
    Join Date
    Jun 2008
    Location
    india
    Age
    39
    Posts
    11
    Rep Power
    0

    Re: York chiller loading issue

    hi

    The system commissioned by service provider of york

  4. #4
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: York chiller loading issue

    It would be worth checking to make sure you have a temperature differential across the evaporator.
    Check flow and pump direction. Some system parameters would be usefull.
    I love the smell of Ammonia in the morning!

  5. #5
    Join Date
    Jun 2008
    Location
    india
    Age
    39
    Posts
    11
    Rep Power
    0

    Re: York chiller loading issue

    The evaporator temperature difference is 8 - 9 deg and we maintain the working pressure of chilled water system is 2 - 3 bar pressure

    rated pump flow is 115 m3 /hr but we didn't measure the actual flow

  6. #6
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: York chiller loading issue

    Hi sensek do you have the system set points and pressure/temperatures? Can you explain your plant requirements too? sorry for all questions but to diagnose faults from a distance all the information you can supply makes it more achievable.
    I love the smell of Ammonia in the morning!

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: York chiller loading issue

    Hi
    pls state your actual temp differntial accros the evaporator ,
    has the system been limited by york not to load over 60%?
    you have a paramter to check this !
    stating system refrigerant pressures could be helpful to.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: York chiller loading issue

    Hi sensek.

    I don't know about your model of York chiller, maybe someone from York has heard if it?

    Anyway that's immaterial, any make of chiller with a half decent controller would unload or restrict the load capacity with a 6 to 8c temperature across it.
    Pump pressure is irrelevant, it's the pressure diff across the evap.
    You don't tell us how old this chiller is?
    Or how long you have had the issue?

    If you can measure the flow (as asked for by the above) then I suspect all will become clear.

    Most makes of chiller you would expect 3-4c diff fully loaded.