    Chiller Thermocold High Pressure alarm. Carel PCO1



    Hi everyone.
    There is a problem.
    Chiller Thermocold AWA ANERSAVE II 2310 ZC SE B(R407; PCO1 Carel controller) shows an alarm
    "AL013 High Pressure Circuit 2(Pressostat)".
    The wiring is OK. Pressure relay: Johnson controls P100CP-1 CO 300Psi(20 Bar) CI 400(27 Bar) with automatic reset. The pressure in the system 2 is 7.5 Bar. There is a signal in PLC terminal DI14H(220V) which responsable for High pressure alarm .The high pressure relay is connected in series with fans klixon (fan thermal protection). But the controller I/O shows on display that digital input 14 are open (there is no signal in DI14H).

    What is it? Dead Controller? Can I solve the problem by restart controller? How can I do it without loss of programm?

    Image0002.jpgImage0003.jpg



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Chiller Thermocold High Pressure alarm. Carel PCO1

    Quote Originally Posted by Hvatit View Post
    Hi everyone.
    There is a problem.
    Chiller Thermocold AWA ANERSAVE II 2310 ZC SE B(R407; PCO1 Carel controller) shows an alarm
    "AL013 High Pressure Circuit 2(Pressostat)".
    The wiring is OK. Pressure relay: Johnson controls P100CP-1 CO 300Psi(20 Bar) CI 400(27 Bar) with automatic reset. The pressure in the system 2 is 7.5 Bar. There is a signal in PLC terminal DI14H(220V) which responsable for High pressure alarm .The high pressure relay is connected in series with fans klixon (fan thermal protection). But the controller I/O shows on display that digital input 14 are open (there is no signal in DI14H).

    What is it? Dead Controller? Can I solve the problem by restart controller? How can I do it without loss of programm?
    Looking at the wiring diagram, I would expect to have an input into DI14H under normal operating conditions, as the fan overloads and HP switch have NC contacts.

    Can you trace the 220v with a multimeter through the fan overloads and HP switch, to see where (and if) it stops?

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: Chiller Thermocold High Pressure alarm. Carel PCO1

    Hi
    check for previous posts on re , occasionaly these "high" inputs using 230 volts stop working and you need to switch to the adjacent input using low voltage 24vac.
    on the pco cotroller hp input is ok when it has 230 volts, when this input opens you will have a fault !
    if you have 230 volt and still tha alarm persists , change the input .
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  4. #4
    Join Date
    Aug 2011
    Location
    Ukraine
    Posts
    6
    Rep Power
    0

    Re: Chiller Thermocold High Pressure alarm. Carel PCO1

    Thanks a lot Goshen and Frank