Thread: Exhaust system On STP Plant Room
-
12-06-2013, 04:33 PM #1
Exhaust system On STP Plant Room
Hi Friends...
would some body help me to design the exhaust system on STP plant room...? or we can design the exhaust as we design for the toilets.or we have to follow the different norms and designing procedures, if so then please help me on this matter..
-
12-06-2013, 10:55 PM #2
Re: Exhaust system On STP Plant Room
Please explain - what does STP stand for?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
13-06-2013, 02:31 AM #3
Re: Exhaust system On STP Plant Room
@Brian.it stands for " Sewage treatment plant "
-
13-06-2013, 08:06 AM #4
Re: Exhaust system On STP Plant Room
Hi Anil you will need to consider that all equipment should be Ex rated for extraction equipment due to the possibility of flammable gases being present. Notably methane will be present and you will require maintaining concentration below 5% (lower flammability range). This can be done with constant ventilation or sample monitoring (most cost effective considerations do apply). 4 - 6 air changes / hour is normal for ventilation capacity but could be as high as 10 - 12 air changes I would recommend you check your local building regulations.