    Exhaust system On STP Plant Room



    Hi Friends...
    would some body help me to design the exhaust system on STP plant room...? or we can design the exhaust as we design for the toilets.or we have to follow the different norms and designing procedures, if so then please help me on this matter..



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Exhaust system On STP Plant Room

    Please explain - what does STP stand for?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: Exhaust system On STP Plant Room

    @Brian.it stands for " Sewage treatment plant "

  4. #4
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Exhaust system On STP Plant Room

    Hi Anil you will need to consider that all equipment should be Ex rated for extraction equipment due to the possibility of flammable gases being present. Notably methane will be present and you will require maintaining concentration below 5% (lower flammability range). This can be done with constant ventilation or sample monitoring (most cost effective considerations do apply). 4 - 6 air changes / hour is normal for ventilation capacity but could be as high as 10 - 12 air changes I would recommend you check your local building regulations.
    I love the smell of Ammonia in the morning!

  5. #5
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: Exhaust system On STP Plant Room

    Quote Originally Posted by hookster View Post
    Hi Anil you will need to consider that all equipment should be Ex rated for extraction equipment due to the possibility of flammable gases being present. Notably methane will be present and you will require maintaining concentration below 5% (lower flammability range). This can be done with constant ventilation or sample monitoring (most cost effective considerations do apply). 4 - 6 air changes / hour is normal for ventilation capacity but could be as high as 10 - 12 air changes I would recommend you check your local building regulations.
    hi Hookster..many thanks for the information.according to you i have to buy the special ventilation fan for exhaust.do you have any booklet for designing the exhaust on this plant room..?