Results 1 to 12 of 12

Thread: DX Evaporator

  1. #1
    Join Date
    Apr 2013
    Location
    England
    Posts
    41
    Rep Power
    0

    DX Evaporator



    Can someone please enlighten me, does this mean Direct Expansion or Dry Expansion? I have looked it up and have found both meanings on here and google.

    I am trying to understand the Coolpak software, which I hope will help me understand the thermodynamics of the various stages of the refrigeration process (vapour compression cycle), which will eventually allow me to understand my project a bit better ? ?

    Would love some help on DX Expansion's real meaning, thank you
    James



  2. #2
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: DX Evaporator

    I've always known Dx as direct expansion myself.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: DX Evaporator

    Direct expansion
    I would assume the Term dry refers to the prefered refrigerant vapour state?
    Grizzly

  4. #4
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: DX Evaporator

    Hi James
    I am the same as mike and Grizzly, I have always known it as Direct Expansion, I would say both terms are correct. In Principles of Refrigeration by Dossat it refers to Dry Expansion where the liquid refrigerant has completely vaporized by the time it reaches the end of the evaporator. In the real world it is referred to as Direct expansion.
    Paul

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: DX Evaporator

    Hi Again.
    Paul's quote, Helps a lot.
    Dry- opposite to Wet!

    On a flooded system the system return is refered to as a Wet return.
    Which is obviously a mix of vapour and Liquid.
    This return is not directly connected to the comp suction.
    So Liquid carry over is not a problem as the return is liquid with flash gas.
    So if the line is refered to as a Wet return, why not call a suction line a dry return?

    Although technically it may well not be so!
    Grizzly

  6. #6
    Join Date
    Apr 2013
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: DX Evaporator

    Thanks guys for replies,
    I will assume it means Direct Expansion in this case then as the software seems to be aimed more towards technicians and uses DX everywhere without explanation, so it must expect people to take its meaning as the more popular one.

    Cheers, James

  7. #7
    Join Date
    Apr 2013
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: DX Evaporator

    Also, what exactly is the meaning of Direct Expansion?

    I have got the meaning of Direct Expansion to mean: 'Evaporator is in Direct contact with the air stream, so the cooling coil of the airside loop is also the evaporator of the refrigeration loop. The term 'Direct' refers to the position of the evap. with respect to the airside loop.'

    I'm a bit confused because airside loop seems to refer only to something in air-conditioning and I can't find it to do with refrigerators.

    Any knowledge is appreciated cheers

  8. #8
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: DX Evaporator

    Quote Originally Posted by jamesk View Post
    Also, what exactly is the meaning of Direct Expansion?

    I have got the meaning of Direct Expansion to mean: 'Evaporator is in Direct contact with the air stream, so the cooling coil of the airside loop is also the evaporator of the refrigeration loop. The term 'Direct' refers to the position of the evap. with respect to the airside loop.'

    I'm a bit confused because airside loop seems to refer only to something in air-conditioning and I can't find it to do with refrigerators.

    Any knowledge is appreciated cheers

    Direct expansion means the refrigerant is directly expanded into the evap.

    The expansion device is connected as close to the evap as possible and the
    refrigerant is directly expanded into the evaporator from that point.

    As others have said in a DX system the liquid refrigerant should evaporate before
    leaving the evap coil and therefore the refrigerant is (or should be) dry when it exits
    the evap coil (hence dry expansion or direct expansion)..
    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  9. #9
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: DX Evaporator

    Quote Originally Posted by jamesk View Post
    Also, what exactly is the meaning of Direct Expansion?

    I have got the meaning of Direct Expansion to mean: 'Evaporator is in Direct contact with the air stream, so the cooling coil of the airside loop is also the evaporator of the refrigeration loop. The term 'Direct' refers to the position of the evap. with respect to the airside loop.'

    I'm a bit confused because airside loop seems to refer only to something in air-conditioning and I can't find it to do with refrigerators.

    Any knowledge is appreciated cheers

    The conditioned air is air off the evaporator, the air that carries the sensible
    and latent heat from the space being cooled and back to the evap is called return air.

    This is the airside loop and is very American.
    We tend to just refer to suply and return air or conditioned air.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  10. #10
    Join Date
    Apr 2013
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: DX Evaporator

    Thank you very much Rob. I have taken all of that in, slowly understanding refrigeration, it is such a LARGE subject its hard to get my head around.
    James

  11. #11
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: DX Evaporator

    Quote Originally Posted by jamesk View Post
    Can someone please enlighten me, does this mean Direct Expansion or Dry Expansion? I have looked it up and have found both meanings on here and google.

    I am trying to understand the Coolpak software, which I hope will help me understand the thermodynamics of the various stages of the refrigeration process (vapour compression cycle), which will eventually allow me to understand my project a bit better ? ?

    Would love some help on DX Expansion's real meaning, thank you
    James
    go to this link,

    http://www.mediafire.com/?mka9bga66ncutr5.

  12. #12
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: DX Evaporator

    Quote Originally Posted by jamesk View Post
    Thank you very much Rob. I have taken all of that in, slowly understanding refrigeration, it is such a LARGE subject its hard to get my head around.
    James
    When I first went back to college to retrain into ac I thought "Whats in an fridge -it stands in the corner and gets cold"

    I know know it's when it doesn't get cold the fun begins...