08-06-2013, 04:45 PM #1
Fan on walk-in cooler condenser won't shut off
So normally, the big fan on the top of our walk-in cooler will cycle on and off along with the condenser. But we are currently having a problem where the fan runs continuously - it never shuts off! The condenser still clicks on and off as necessary to control the walk-in temperature, but the big loud fan never stops. When the fan is incorrectly stuck in the ON condition, I can tap the big metal control box next to the fan and it will stop. So whatever is responsible for stopping the fan is sticking somehow, and when I hit it, it releases and stops the fan.
Can anyone clue me in as to which component I need to replace to solve this problem?
-
08-06-2013, 05:10 PM #2
Re: Fan on walk-in cooler condenser won't shut off
The fan relay...
-
08-06-2013, 05:17 PM #3
Re: Fan on walk-in cooler condenser won't shut off
contactor /relay stickin
-
08-06-2013, 06:33 PM #4
Re: Fan on walk-in cooler condenser won't shut off
Sounds like fan speed controller, relay or contactor dependant on what controls the motor.
-
08-06-2013, 08:38 PM #5
Re: Fan on walk-in cooler condenser won't shut off
Fan doohickey.
Mostly found in Oxfordshire, UK :)
-
09-06-2013, 07:25 PM #6
Re: Fan on walk-in cooler condenser won't shut off
Thanks for the help guys. It sounds like the consensus is the contactor/relay.
Here is a photo of the contents of the control box:
http://goo.gl/rnyA5
I'm assuming the faulty part is the thing at the top (labeled "C1"). Right?
Here's a close-up:
http://goo.gl/Lyt1P
Any other troubleshooting advice? Can I lubricate it or something to stop it from sticking?
-
09-06-2013, 07:58 PM #7
Re: Fan on walk-in cooler condenser won't shut off
does c1 contactor feed the fan or compressor and fan? as there 2 lots of fuses- usually 3ph oncompressor and 2 phase for the fan
-
09-06-2013, 10:46 PM #8
Re: Fan on walk-in cooler condenser won't shut off
I think the contactor feeds both the compressor *and* the fan. The bank of three fuses on the left feed the compressor while the bank of two fuses on the right with the smaller gauge wires feeds the fan.
So if the compressor is cycling fine but the fan is not, then the contactor is probably OK and the problem is elsewhere, right?
-
09-06-2013, 11:02 PM #9
Re: Fan on walk-in cooler condenser won't shut off