    Cryogenics -80



    Hi can anyone help i need to find out the refrigerant charge as the unit that a compressor change,the refrigerant says mixture and amount of 0.260 Grams.I have spoken the the uk importer and he has no info on.
    Its a single stage unit that only needs one compressor with two circuits (like a cascade system)
    Unit detail
    Make-zhongke meiling cryogenics
    Model-DW-HW50
    Ps i have removed the refrigerant which has a smell of propane

    Could i use R508b ?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Cryogenics -80

    r290,r600 mix or 5o8b usually -80 kit is 2 stage cascade- 404a for high stage
    no nameplate on the cabinet?
    last resort check with manufacturers as if it doesnt work its gonna take ages to get to temp

  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Cryogenics -80

    Propane keeps the oil flowing, it'll need a small amount from vacuum, maybe only a gauge line full. Recommended charge and type of refrigerant is vital, don't guess at -80. Sounds chinese so god only knows what was in it originally.